I'm getting ready to run wiring for a 18,000 BTU mini-split AC for my garage. Reading the manual it says the following:
Install a surge protector and a disconnect switch box, and a dedicated circuit breaker with a capacity of 1.5 times the maximum current of the unit.
A properly rated HACR-type fuse or circuit breaker that disconnects all poles and has a contact separation of at least 1/8in (3mm) must be incorporated in the fixed wiring. The qualified technician must use an approved circuit breaker or fuse.
Minimum circuit ampacity - 15A
Max fuse - 20A
So what do i need? My guess is 2 pole 240V 20A breaker with 12/2 wiring into a fused (30A) disconnect box, with a 12 gauge whip to the unit.