I'm at the rough wiring stage in my detached garage. I"m planning to add a mini-split air conditioner/heat pump later on, and I'd like to run the wire for it while the walls are still opened up. I haven't made a final selection for make and model yet, but the following stats are for what would probably be the largest one I would potentially be using (one outside unit servicing one head unit inside the garage):
Electrical .......................... 208/230 V AC 1ph-60HZ
Available Voltage Range.............. 187 - 253 V +/- 10%
Max Fuse Size........................ 30 A
Max Operating Current (Evaporator)... 15.5 A
Max Starting Current (Condenser)..... 10.5 A
Input Power:
Cooling.............................. 1.76 kW
Heating.............................. 1.94 kW
Running Current:
Cooling.............................. 7.9 A
Heating.............................. 8.6 A
Capacity:
Compressor........................... Rotary x1
Motor Output......................... 2,100 W
Fan Motor
Type: DC (condenser)................. Propeller x1
Type: DC (evaporator)................ Cross flow fan x1
Motor Output (condenser)............. 100 W
Motor Output (evaporator)............ 53 W
Would 12 gauge copper (12/2 NM-B) be proper for this application, or should I use something larger, such as 10 gauge? The length from the breaker panel to the outside unit disconnect would be 25 feet.
Thank you!
Electrical .......................... 208/230 V AC 1ph-60HZ
Available Voltage Range.............. 187 - 253 V +/- 10%
Max Fuse Size........................ 30 A
Max Operating Current (Evaporator)... 15.5 A
Max Starting Current (Condenser)..... 10.5 A
Input Power:
Cooling.............................. 1.76 kW
Heating.............................. 1.94 kW
Running Current:
Cooling.............................. 7.9 A
Heating.............................. 8.6 A
Capacity:
Compressor........................... Rotary x1
Motor Output......................... 2,100 W
Fan Motor
Type: DC (condenser)................. Propeller x1
Type: DC (evaporator)................ Cross flow fan x1
Motor Output (condenser)............. 100 W
Motor Output (evaporator)............ 53 W
Would 12 gauge copper (12/2 NM-B) be proper for this application, or should I use something larger, such as 10 gauge? The length from the breaker panel to the outside unit disconnect would be 25 feet.
Thank you!