Can I safely run a 5hp RPC on a household 220v dryer circuit w/ 30 AMP breaker? + Its about 60 feet away.
 
To avoid these ads, REGISTER NOW!

89GLH

Well-known member
Joined
Mar 24, 2011
Messages
1,057
Location
Westminster, MD
My Quincy is running on a 30A breaker I swapped in from a 20A baseboard heater parking spot, and it's about 60 feet away.
 
To avoid these ads, REGISTER NOW!

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,927
Location
oregon
http://www.arco-electric.com/AmpSizingAssistance.aspx

I see you posted on the PM site also. In looking around the PM site I was directed to the above site. Doing some searching around the above site should get you the answers you need. They do have converters recommended by FLA (full load amps) of your load and from there you can go to the installation guide to check on the input requirements for the converter.

lg
no neat sig line
 
OP
S

sthojlft

Banned
Joined
Apr 5, 2011
Messages
63
Success-
Dedicated 50A panel in garage fed by #6 wire.
Elimia 10hp RPC.
Works like a charm.