Rules for conduit and SER entering a junction box?

MTWallet

Member
Joined
Apr 20, 2016
Messages
12
I need to transition between SER in the house to a conduit run of XHHW-2. I intend to do it with terminal blocks in a 10x10x4 metal junction box set in the exterior wall of my attached garage with the access panel facing the inside of the garage. Planning on bringing the SER down through the top of the box (with appropriate wire clamp) and then having the XHHW go out of the back of the box and through the exterior wall in 2" rigid conduit to a metal lb body, then down into the ground with EMT, transitioning to pvc at ground level.

I saw in a thread somewhere that bringing something into the back of a breaker panel was a no-no, does this also apply to a junction box?

Also, is there a requirement on the size box I need to use? I chose the 10x10x4 because it will sit flush with the wall after it is installed, but I can go bigger or deeper if necessary. Thank you!
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Basically the box is supposed to be sized 6X the largest conduit entering the box, so 2in would normally require 12X12 box. There is no restriction I know of on coming in through the back of a panel or box. What size wire are you using?
 
To avoid these ads, REGISTER NOW!
OP
M

MTWallet

Member
Joined
Apr 20, 2016
Messages
12
what size wire are you using?

3x 1/0 alu & 1x #2 alu

Some extra room certainly wouldn't hurt. I've sourced a 12x12x4 that I will pick up tomorrow. Thanks for the feedback!
 