I installed my XPR-10 about a month ago. When I ran the the power to the lift I decided to install a disconnect box on the power side column to give myself a quick method of securing the power if need be. My cousin and I were under the lift looking for a grounding problem on my truck when the lift powered on and started to go up! No one around the controls, I was able to get to the disconnect to stop it. After calming down a bit we did some investigating. Disconnected one side of the push button and turned the power back on and up she went. We figured it must have been the relay (microswitch) that the push button is connected to that failed. Called Bendpak twice no return call, called Jessica from M & J Distributing she called Bendpak. Got a call from Bendpak pretty quick, they said there was a problem with some of their relays. He said he would ship me another one on Monday. With all of that I guess what I'm saying is I would suggest that you install a disconnect somewhere fairly close to your lift. My main panel is about 40 feet from my lift. By the way I love my lift!
 
To avoid these ads, REGISTER NOW!

T_R

Well-known member
Joined
Jul 2, 2015
Messages
902
Location
Maine
I've had it happen at work. The button stuck and the lift took off in the bay the next to mine with a car on it. That lift had a disconnect and we hit it. The rest of the lifts don't. It's not a bad idea. You can just yank the power cord out too.
 

sublimate

Well-known member
Joined
Aug 4, 2010
Messages
776
Location
Colorado
When I ran the the power to the lift I decided to install a disconnect box on the power side column to give myself a quick method of securing the power if need be.

Can you post pics? I need to do this.
 

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
13,639
Location
Lebanon, TN
That is a strange thing for a "relay" to do. They will fail "on" and not shut off, they will fail "off" and not allow operation, but to just turn on by themselves.... that is a almost unheard off.

You mention micro-switch and relay - they are not the same thing. Which part is it that Bendpack is replacing and says "there was a problem with some of their relays" ?

I would want more explanation than that. Glad you had the disconnect.
 
Last edited:

PoorOwner

Well-known member
Joined
Feb 10, 2007
Messages
5,032
Location
CA
so this can happen even if you were not there it could just shoot straight into the roof At anytime?

using a second relay and ceiling switch you would be able to cut the power to the pump power line too.
 

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
13,639
Location
Lebanon, TN
so this can happen even if you were not there it could just shoot straight into the roof At anytime?

using a second relay and ceiling switch you would be able to cut the power to the pump power line too.

You could do something along those lines, but why should you have to? Something is rotten in Denmark regarding this problem to begin with. Devices like this lift should not just startup without someone pushing the start button. Does anything else you own that is electrically powered start without our turning on the switch - with the possible exception of things like air compressors and heating systems?
 

Matt M PA

Well-known member
Joined
Oct 21, 2008
Messages
3,174
Location
SE PA
I did this on my 4 post...I read (I think on these forums) that the button could stick "on"...sorry for the crooked pic...posting from my phone...
 

Attachments

  • image.jpg
    image.jpg
    12.9 KB · Views: 188

kabinenroller

Well-known member
Joined
Sep 14, 2013
Messages
895
Location
S.E. Wisconsin USA
BendPak has a problem. The push button on my lift sticks periodically, I have taken it apart and lubed the button and it helps but the button just actuates a micro switch which could stick. I have a twist loc cord cap on my power cord but know I plan to install a disconnect on the power box.
I do not think I will purchase a BendPak again. There are too many "features" that I dislike. The ladders for the pawl locks are not contained in the uprights so they "clang" on the sides of the posts. Also the locks are very difficult to adjust and synchronize, if adjusted with the lift empty they work different when it is loaded.
I am very cautious when lifting one of my vehicles, when I raise it and then lower it onto the locks I check to make sure each cable is slack. ( which means the Pawl is engaged)
My lift was installed by a BendPak authorized installer, so you would think it is done correctly.
 

T_R

Well-known member
Joined
Jul 2, 2015
Messages
902
Location
Maine
The sticking switch I would be worried about. Noise and locks not engaging probably only matter to a homeowner type user. In a shop nobody cares about noises and nobody uses the locks.
 

fordnut85

Well-known member
Joined
Sep 6, 2012
Messages
231
That would scare the **** out of me :shocking: Glad no one was hurt or anything damaged.

The sticking switch I would be worried about. Noise and locks not engaging probably only matter to a homeowner type user. In a shop nobody cares about noises and nobody uses the locks.

I have to disagree, If any of my guys are caught not setting a lift down on the locks they only get one warning before termination. Also, my guys don't need to listen to a constant clanging every time one goes up on the rack. I know it sounds trivial but they have enough distractions and a hard enough job as it is, they don't need to go home every night looking for tylenol to kill the headaches from a noisy work enviroment.:thumbup:
 

tractordude

Well-known member
Joined
Nov 16, 2009
Messages
2,226
Location
WI
My forward lift will do this when its humid out. The owners manual states it must have a disconnect close to the push button.
 
To avoid these ads, REGISTER NOW!
OP
J

jpig

Active member
Joined
Dec 19, 2010
Messages
25
Location
Tazewell TN
The wiring diagram in the manual calls it the push button microswitch but the push button and the microswitch are two different things. If that makes any sense. The man from Bendpak is the one that called it a relay. Hope he sends the right part. Every time I was done using the lift I would pull the disconnect and glad I did, can't imagine what would have happen had it failed and no one around. Yes I can, the lift would go up, cylinders would extend fully and relief valve would unseat, pump would keeping pumping causing everything to over heat and result in complete pump failure.
 

Theruse

Well-known member
Joined
Aug 12, 2012
Messages
341
Location
Maryland
bendpak cutoff.jpg

I had also heard of these problems. So I added both a cut off switch and and outlet on the bendpak column. Since I wanted to be able to move the lift I mounted the two boxes on magnetic tool holders strips I purchased at HF. This way if I want to move the lift i unplug the motor unit and pull the magnet with the two outlet boxes off the column. As a precaution I turn off the cutoff switch when not in use, so no issue of a rogue relay.
 

holdover

Well-known member
Joined
Feb 15, 2011
Messages
750
Location
VA
problem or not, I put in a dual pole switch that disconnects power to the lift motor, when I installed the lifts seven years ago. My lifts are powered from above and the switch is slightly above the motor in easy reach for an adult. Never had an emergency where I had to use it, BUT I shut the lifts off with the switch when not in use in case the grand kids try to play with it, even thought they have been told not to be in the garage without an adult. My dad always used the expression "an ounce of prevention is worth a pound of cure" your mileage may vary
 

Bellaireroad

Well-known member
Joined
Mar 22, 2013
Messages
636
Location
Fort Worth
I installed my XPR-10 about a month ago. When I ran the the power to the lift I decided to install a disconnect box on the power side column to give myself a quick method of securing the power if need be. My cousin and I were under the lift looking for a grounding problem on my truck when the lift powered on and started to go up! No one around the controls, I was able to get to the disconnect to stop it. After calming down a bit we did some investigating. Disconnected one side of the push button and turned the power back on and up she went. We figured it must have been the relay (microswitch) that the push button is connected to that failed. Called Bendpak twice no return call, called Jessica from M & J Distributing she called Bendpak. Got a call from Bendpak pretty quick, they said there was a problem with some of their relays. He said he would ship me another one on Monday. With all of that I guess what I'm saying is I would suggest that you install a disconnect somewhere fairly close to your lift. My main panel is about 40 feet from my lift. By the way I love my lift!

Wow.....this sounds like a tragedy waiting to happen.
I'm surprised a Bendpack representative told you that there was a problem with some of the relays and a recall has not been done.
 

vision8

Well-known member
Joined
Jan 19, 2012
Messages
124
Location
Southern Ontario Canada
Our electrical code requires a disconnect within eye-sight of the lift. My Rotary has a toggle switch for the motor and i will feed the hoist from a disconnect 12 feet from the motor.
Cdn codes are for an industrial application.
Al in Dundas
 

WhiffySpark

Well-known member
Joined
Oct 22, 2009
Messages
6,252
so this can happen even if you were not there it could just shoot straight into the roof At anytime?

using a second relay and ceiling switch you would be able to cut the power to the pump power line too.

Not really.. There's a cutoff switch at the top.

I had a lift that had a button stick all the time. You had to smack it to get it to stop. Owner didn't care.
 

workhurts

Well-known member
Joined
Mar 5, 2006
Messages
277
Location
VA
Not really.. There's a cutoff switch at the top.

I had a lift that had a button stick all the time. You had to smack it to get it to stop. Owner didn't care.


Cut-off switch at the top of what? I don't see any sensors or anything on the bendpak and even if there were, by the time it got to the top I think my car would be a little squished.

I usually pull the power or just turn off the breaker when on vacation but I'll be doing that all the time now in case it decides to do it's own thing when I'm not at home.

While working on it, I can unplug it if it gets crazy.
 

WhiffySpark

Well-known member
Joined
Oct 22, 2009
Messages
6,252
Cut-off switch at the top of what? I don't see any sensors or anything on the bendpak and even if there were, by the time it got to the top I think my car would be a little squished.

I usually pull the power or just turn off the breaker when on vacation but I'll be doing that all the time now in case it decides to do it's own thing when I'm not at home.

While working on it, I can unplug it if it gets crazy.

There should be a bar on the bottom of the cross bar. When roof touches that it shuts off. All the ones I've seen are mechanical, they pull something out of the switch housing when it touches.
 

workhurts

Well-known member
Joined
Mar 5, 2006
Messages
277
Location
VA
There should be a bar on the bottom of the cross bar. When roof touches that it shuts off. All the ones I've seen are mechanical, they pull something out of the switch housing when it touches.

Was thinking bendpak in general. I have a 4 post ... no crossbar.
 

WhiffySpark

Well-known member
Joined
Oct 22, 2009
Messages
6,252
No no cross bar on 4 posts. Never seen any safety items on 4 posts except for the locks. But even those ****. If you're not paying attention you can end up missing the lock on one post when lowering. Hunter machines will beep until you fix it

Most people with 4 posts have the ceiling space so no safety's needed
 

volaredon

Well-known member
Joined
Oct 7, 2012
Messages
1,608
Location
IL
at an old employer we had 4 Rotary lifts, all 2 post and on one, I replaced the switch at least 2-3 times during the 10 years I'd worked there, 2 of the 4 lifts were brand new within a year before I went to work there in a brand new expansion of the shop, it was on one of these 2 newer Rotarys (these lifts are 22 years old now, IDK of any issues in last 11 years since its been that long since I worked there LOL) The older 2 never had a problem in the time I was there, one of the 2 newer ones though did,,,
the switch would stick "on" when pushed, never did its trick by itself, only when the button would be pushed. It did raise all the way to the stop bar one time that I remember before I could get to the breaker 15 feet away, no damage.
 

tractordude

Well-known member
Joined
Nov 16, 2009
Messages
2,226
Location
WI
There should be a bar on the bottom of the cross bar. When roof touches that it shuts off. All the ones I've seen are mechanical, they pull something out of the switch housing when it touches.

I have a forward 2 post floor plate model, no top bar. You need a manual disconnect on ALL lifts.
 
OP
J

jpig

Active member
Joined
Dec 19, 2010
Messages
25
Location
Tazewell TN
I received my replacement switch yesterday installed it today and everything worked just fine. Bendpak said they would send the part out on Monday but I received it on Monday kudos to Bendpak. Also a big thanks to M & J Distributing for their help. My advice to anyone putting in a auto lift install a disconnect box within arms reach. I think Bendpak should include one for each unit they ship!
 