Like the title says I'm running service to my shop from my existing 200amp panel in my house. I'll be running 4 #3 wires (copper) in conduit all the way and it will be buried. Two questions:

1. The conduit with the new wire will cross over the existing direct burial wire that feeds my main 200amp service. Is it ok that they will be close to one another (not touching though obviously)?

2. For conduit size, is 1.5" sufficient or should I run 2"?

Thanks,
Matt
 
To avoid these ads, REGISTER NOW!
OP
M

ml504

Well-known member
Joined
Mar 19, 2008
Messages
99
Anyone have advice on crossing wire paths undergound? I can't find anything that says not too, just would like some extra input. Thanks...
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Like the title says I'm running service to my shop from my existing 200amp panel in my house. I'll be running 4 #3 wires (copper) in conduit all the way and it will be buried.

You don't need four #3's, you only need three, with a #8 green.

1. The conduit with the new wire will cross over the existing direct burial wire that feeds my main 200amp service. Is it ok that they will be close to one another (not touching though obviously)?

Should be fine. God help you though if you hit the power co. wires.....

2. For conduit size, is 1.5" sufficient or should I run 2"?

It'd fit in an 1.25" easily, if you want to go larger you certainly can.
 