It's not the cost of the panel. It's the 300ft of wire that's gonna get you. I recently added a sub-panel to a separate storage building. Mine was only about 100ft from the house. I rented what I thought was a large enough trench digger from home depot but the soil is very hard and rocky so we had quite a bit of trouble digging the trench. It doesn't sound like you'll have that issue.
If the local electric company will run a separate meter to your garage, then I'd have them do that. If not, I'd go with aluminum wire over copper. I used 6 gauge aluminum xhhw-2. I felt like I only needed 50 amps but if you're looking for 125, you'll probably need to go with 2/0.
I paid just over $100 for the wire. If I had gone with copper, it would have been well over 3 times the price.
It's a one time expense of about $400 to go from #2 mhf to 2/0. Another $400 to move to 4/0. Not exactly an earth shattering sum to someone building a 30x40 shop.

I'd bump up to at least 2/0 if this was my shop.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
I know 2 gauge thwn wire is rated at 130 amps. I don't know what gauge it would have to be for a 300ft run underground though.
youre looking at the wrong column. you cannot protect #2 cu with a 130a breaker. the 90° column is for derating only. #2 cu is good for 115a
You want to use a voltage drop calculator to determine gauge required.

If you are considering running copper, I would strongly recommend rethinking that. Aluminum will be a fraction of the cost
or just use the formula i posted in the FAQ sticky. gotta be careful with some online calculators as they output a larger wire than is necessary.
I ran 250 ot triplex for 200 amp service 300 ft out to my building no problems ata ll
no such thing as 250 ot (sp) wire. its 250mcm or KCMIL and triplex is not only the wrong # of conductors unless wired before 2008 but its usually single rated URD which is not permitted inside buildings. its not even an NEC recognized cable type.
 

frankd

Well-known member
Joined
Aug 5, 2014
Messages
677
Location
Long Island, NY
It's a one time expense of about $400 to go from #2 mhf to 2/0. Another $400 to move to 4/0. Not exactly an earth shattering sum to someone building a 30x40 shop.

I'd bump up to at least 2/0 if this was my shop.

I agree, not an earth shattering sum but the little things add up. For my purposes, I felt like 50 amps was already overdoing it so I didn't see a need to go with larger wire. I also couldn't find a valid reason to go with copper over aluminum.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,847
Location
Richmond, VA
I agree, not an earth shattering sum but the little things add up. For my purposes, I felt like 50 amps was already overdoing it so I didn't see a need to go with larger wire. I also couldn't find a valid reason to go with copper over aluminum.
We all have our own budgets and priorities.
 

inphx

Well-known member
Joined
Feb 23, 2012
Messages
1,287
Location
Phoenix/Scottsdale AZ
A bit off topic but while you have the trench add a second conduit in case you later want to add solar panels on the garage and feed back to the house. Im redigging my trench a few years later. And also drop in some direct bury cat6 wire.
 
To avoid these ads, REGISTER NOW!
OP
H

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
A bit off topic but while you have the trench add a second conduit in case you later want to add solar panels on the garage and feed back to the house. Im redigging my trench a few years later. And also drop in some direct bury cat6 wire.
Or an oversized one.
 

pelletman

Well-known member
Joined
Apr 5, 2016
Messages
1,267
Location
Worcester, People's Republic of Massachusetts
Im liking this idea. Just put the second building 300ft away put a vehicle lift inside it and just buy another air compressor for that building too. That was the reason for connecting the two buildings was to make it so all my tools stay in one building, but I guess it's not that big a deal to just have a second smaller toolbox another compressor etc.
Plus you get to buy more tools!
 
OP
H

Hobby_Man22

Well-known member
Joined
Nov 16, 2020
Messages
3,581
Location
tx
I missed that part. The coax and internet cable don't have to be in conduit do they?
 