running 2 branch circuits thru 1 outlet box?

Redwolf947

Well-known member
Joined
Feb 13, 2015
Messages
613
Location
South East WI
Soon I plan to rewire my garage. Can I run 2 separate circuits in or through a 2 gang 2 receptical (quad outlet) box to the next and so on? This would be to separate the loads. Example say i have a space heater plugged in one side and I have my shop vac on the other I know I won't trip the breaker this way. I think some kitchens are wired like this? Or is this me over thinking this?? I plan on 12-2 wire with 20a breakers. I tried the NEC I think it says I can. Just want to make sure.
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
If its passing thru you don't want to tie the breaker. This is an indication that it is a part of a MWBC which is not the case here.
 

toplessHO

Well-known member
Joined
Oct 20, 2014
Messages
14,054
Location
central florida
and make sure if its got a shared neutral on multiwire system to have that pigtailed.