first off the basics we have 200 amp service to the house and adding another meter is not practical based on the location of the hookup. we are just about out of space in our house panel.

we have a pool out back and it has a outdoor panel the pump runs under 20amps and there is a pool light also I believe its 15 amps. when I put my building up the wire from the house to the building will run right next to this pool subpanel. I was thinking it may make sence to re do the wiring and run a larger outdoor subpanel to the pool. then run off the outdoor subpanel to my building. this way I wont have to run conduit threw the house for the service wiring. the building will probly be a 100 amp service and a distance of about 125 foot. away from the pool panel perhaps less depending on panel location
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Remember to account for possible voltage drop for distance. You need to consider the distance from the main panel to the first sub and then the distance from the first sub to the second sub. In other words the feed to the first sub needs to be able to handle the load to the second sub.
 
OP
J

justin1795

Well-known member
Joined
Aug 7, 2013
Messages
442
Location
blue grass IA
i was wondering about that. perhaps do 125 amps to the pool panel. my question is will the wire fit into the breaker? i would probly be at 2/0 wire.
 
To avoid these ads, REGISTER NOW!
OP
J

justin1795

Well-known member
Joined
Aug 7, 2013
Messages
442
Location
blue grass IA
That would be good. I have a buddy who has 2 90 foot pieces of copper 2/0 he will sell to me at scrap value. I probly only have a 40 foot run so I will just have to buy a ground wire
 

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,645
Location
Northeastern CT
You have a total of 180 feet, and need 160 feet total. You have plenty of wire. Buy a roll of white electrical tape, to identify the neutral, and you are home free for the price of a roll of white tape.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Because the ungrounded are increased in size, the grounding conductor has to be increased in size, per NEC article 250,122(B).
 