Running branch circuits

kool55

Well-known member
Joined
Aug 25, 2007
Messages
382
Location
South Central VA.
My 200 amp main panel is 80 ft. from where alot of electrical items will be. Parts room with air compressor,tankless propane water heater, etc. I am also thinking of locating my band saw and bridgeport in that area too.I think I should have a sub panel installed in the parts room and run circuits off of it.That would eliminate long wire runs. Sound ok?:headscrat
 
To avoid these ads, REGISTER NOW!

Kevin54

MEMBER EMERITUS
Joined
Jan 12, 2005
Messages
29,341
Location
Urbana, Ohio
I would. By doing that, you are running one larger line to the sub, instead of a bunch of heavier lines to where you need them. It would probably save quite a bit in $$$.
 

MXtras

Well-known member
Joined
Aug 17, 2005
Messages
1,356
Location
On the Right Coast
That would be the correct way to do it. It would add a lot of flexibility in that distant area, too (easier to add a new circuit later).

Scott
 

Ezzie

Well-known member
Joined
Oct 15, 2007
Messages
371
Location
Lake Chapala, Jalisco
Yup, that's the way I did it as well. 200A service entrance and main panel feeds most of the building lighting, 110V and 220V receptacles and boiler, air compressor in the "mechanical" room, 100A sub panel off the main panel for the workshop area (lift, machinery) that is about 60' away. Gives lots of flexibility if you want to add extra machinery later on.
 
OP
K

kool55

Well-known member
Joined
Aug 25, 2007
Messages
382
Location
South Central VA.
Thanks guys, now I just need to figure out the amp capacity sub panel [100?]and the wire guage for the feeders. I will run it up above the ceiling in non metalic conduit and down into the parts/ compressor room.

Hey Scott. I am getting close to hooking up my vfd for the Bridgeport. I will try to find your writeup when you did yours. Glenn
 

ng8264723

Well-known member
Joined
Aug 28, 2006
Messages
743
Location
Oakham MA
I bought the Black and decker home wiring book when I first installed a subpanel. It is a great book and very informative. I ran a 100amp sub to my barn. I used 2/3 wire (alum). It was around 120 feet away. It has worked great for a few years now. I would definaately recomend at least a 100amp sub. The B and D book has all the necessary guages for the amps your running. It is easy to read and has great circuit diagrams.
 

boiler7904

Well-known member
Joined
Apr 4, 2006
Messages
3,414
Location
NW IN
A subpanel near the main electrical loads also makes shutting off a circuit easier than walking through the house to get to the panel.
 
To avoid these ads, REGISTER NOW!

locomike

Well-known member
Joined
Nov 16, 2007
Messages
149
I'm not the only one with that book a? Glad to see I wasn't the only electrical rookie!
 
OP
K

kool55

Well-known member
Joined
Aug 25, 2007
Messages
382
Location
South Central VA.
OK, I think I have it figured out. Since I have a Cutler Hammer 200amp ch loadcenter now I will use a Cutler Hammer 125 amp main lug center with 16 spaces and their 3 pole single throw disconnect switches for the compressor, Bridgeport , band saw and future lathe. Feeder line will be Southwire copper SER 2-2-2-4 .I wanted 100 amp capacity but thought 125 would give me some cushion. Have I overlooked anything?
 
OP
K

kool55

Well-known member
Joined
Aug 25, 2007
Messages
382
Location
South Central VA.
I spent the best part of today calling electric supply houses in the area along with stopping lowes and Home Depot and could not find 2-2-2-4 copper feeder SER. Everybody has AL.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I spent the best part of today calling electric supply houses in the area along with stopping lowes and Home Depot and could not find 2-2-2-4 copper feeder SER. Everybody has AL.

Personally, I've never seen copper SER, only heard of it. But, any decent electrical supply house should be able to get it for you. Otherwise, 1/0 AL ser will get you 100 amps too, if they can get that for you instead. 2/0 AL will get you to a 125 amp breaker, if you're calculated load is under 115 amps.
 