Running a 220v line 100' to my shop underground. Just need around 60 amp. What size alum wire should I use.
Should I run it in conduit?
 
To avoid these ads, REGISTER NOW!

wnstwolf

Well-known member
Joined
Nov 7, 2007
Messages
837
Location
New York and PA
Aluminum for mains is common but I would say your application is not a main more of a sub panel off your main house service? I think you can get a 2-2-2-6 wire at lowes / HD for this the ground is a bit smaller than the conductors may be overkill but not sure what their next size is?. At 100' lay the pipe added protection if you can if not make sure your strap it so nothing can hit it later!
 
To avoid these ads, REGISTER NOW!
OP
S

skyking

Well-known member
Joined
Jun 26, 2012
Messages
1,856
Location
Dallas & Tulsa
I never have really understood why you have a ground and a common.Dont they both go to ground .The common bar goes to ground doesnt it?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You need to look over at the Electrical forum. You'll get a lot of good info for sub panel feeds.

You can go with Aluminum 2-2-2-4 or 2-2-4-6 Mobile Home Feeder (MHF) and that will be good for up to 90A for your 100'. You need four conductors because an equipment ground is required to be run between the main and sub. The sub will require the addition of a ground bar because the ground and neutral are not bonded in the sub. The existing neutral/ ground bar in the sub will need to have the case bonding screw removed. And also you need to install two 8' ground rods 6' apart from each other connected by #6 bare copper to the ground bar in the sub.

For just 60A you can use #4 Al THHN/THWN or #6 Cu THHN/THWN.

*
 
Last edited: