kohner
Member
All right folks, I have spent countless hours researching and think I understand this, but I'd really like someone to proof my electrical plan. A "Relative" was supposed to help me with this, but I think he has told me wrong already as he advised I only run 3 conductor wire instead of 4 to the sub-panel.
I have a new 40x64 pole barn that is about 60 feet from the house. I already have 2" conduit run between for the cable. From the main house panel I will have a 100 amp breaker and use 2-2-2-4 AL Mobile Home Feeder (see pic) to the sub-panel in the barn. The sub-panel at the barn has a removable bridge between the neutral and ground bars that I will remove leaving the neutral separated from the ground. The ground side is bonded to the panel. I will also run a #6 solid copper ground to 2 ground rods outside the barn.
Does this make sense? What am I missing? Where the conduit comes into the house there will be about 12 ft of cable running inside the house before the main panel. Since the cable says indoor/outdoor can I do that or does it need to be in conduit in the house? Can this cable be in conduit between buildings? I appreciate any advice. I will also be consulting an electrician before everything gets turned on, but want to get started on this.
I have a new 40x64 pole barn that is about 60 feet from the house. I already have 2" conduit run between for the cable. From the main house panel I will have a 100 amp breaker and use 2-2-2-4 AL Mobile Home Feeder (see pic) to the sub-panel in the barn. The sub-panel at the barn has a removable bridge between the neutral and ground bars that I will remove leaving the neutral separated from the ground. The ground side is bonded to the panel. I will also run a #6 solid copper ground to 2 ground rods outside the barn.
Does this make sense? What am I missing? Where the conduit comes into the house there will be about 12 ft of cable running inside the house before the main panel. Since the cable says indoor/outdoor can I do that or does it need to be in conduit in the house? Can this cable be in conduit between buildings? I appreciate any advice. I will also be consulting an electrician before everything gets turned on, but want to get started on this.