Running Electrical with Ethernet

MiGarage

Member
Joined
Sep 10, 2013
Messages
7
Good afternoon. I am having a 40x60 pole barn built. We will be trenching and running electrical and water out to barn. I would like to run Ethernet cable as well in the same trench. What would be the best method of doing this to not have interference. Separate conduit for Ethernet? Thanks for the help in advance.
 
To avoid these ads, REGISTER NOW!

Jking24

Well-known member
Joined
Feb 27, 2018
Messages
258
I think they recommend around 6" separation when running in the same space such as a wall cavity and they prefer crossings be a close to 90°as possible. As long as your inspector is good with it witch i see no reason he wouldn't be. I don't see it being a problem in a seperate conduit in the same trench
 
To avoid these ads, REGISTER NOW!

jdm5

Well-known member
Joined
Jan 1, 2012
Messages
281
Location
CT
Definitely separate conduit for multiple reasons...your ethernet would need to be rated at the higher voltage for electrical, and you risk crosstalk running parallel to electrical.

Run an additional oversized conduit to future proof it (1", 2", whatever you are willing to do).

You don't say how long a run you have, ethernet is good to 100m (~330 feet). Fiber can go considerably more...would recommend looking at Ubiquiti equipment which can easily do fiber, is reasonably priced, and is low-end enterprise grade but easy to setup.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,625
Location
BC
If the power cable is metallic-armoured, or the Cat 5/6 is shielded, it further reduces interference.
 

Paul_The_Builder

Well-known member
Joined
May 9, 2020
Messages
217
Location
Dallas, TX
Keep them in separate conduits and you'll be fine.

If you open up the ceiling of most commercial buildings, you'll see Cat5/6 criss crossing 120/277v power conduits all over the place.

No need to go crazy with shielded cat6 or anything. You'll be fine.
 
OP
M

MiGarage

Member
Joined
Sep 10, 2013
Messages
7
The run is about 150-200’. I will run in separate conduit and try to space 6” away from other power line.
 