Running metal conduit / outlets outside the drywall

pipsters

Well-known member
Joined
Sep 1, 2010
Messages
4,899
Location
USA
I have a garage with now one dedicated 20 amp circuit in it and one 15 amp circuit for all the other stuff (lights, garage door opener, etc).

That one 20 amp circuit has one outlet on it. What I would like to do is run some electrical outlets around my garage but the garage has been drywalled.

So I think I can do this legally (not sure about code, this is what I am concerned about) by using the metal conduit and metal boxes. I'm not sure how to begin researching how this is done however. Ie what height does it need to be at etc.
 
To avoid these ads, REGISTER NOW!

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
yes you can do that. no particular height is needed. to be code the outlets need to be gfci protected. support the conduit within 3 ft of every box and no more than 10 ft between supports. ground all boxes. use raised industrial covers for the outlets.
 

Jim Johnstone

Well-known member
Joined
Apr 11, 2011
Messages
1,841
Location
Brantford, Ontario
yes you can do that. no particular height is needed. to be code the outlets need to be gfci protected. support the conduit within 3 ft of every box and no more than 10 ft between supports. ground all boxes. use raised industrial covers for the outlets.

Would the same general rules apply if one were to do the same using flexible conduit rather than rigid conduit?

I'm planning on putting all my outlets and lighting under the drywall, but I am thinking of using surface mounted conduit for all my 240 volt applications so I have the option of moving them if I shift around my machines, or even pulling it all off and taking it with me if I was to move.
 

vhol5

Well-known member
Joined
May 24, 2011
Messages
359
Location
West Texas
yes you can do that. no particular height is needed. to be code the outlets need to be gfci protected. support the conduit within 3 ft of every box and no more than 10 ft between supports. ground all boxes. use raised industrial covers for the outlets.

X2 with Jason. Also, if you decide to use handy boxes, make sure you also use handy box COVERS in the outlets. Makes for a smoother look!


On edit, flex, looks terrible on the outside of drywall...
 
Last edited:
To avoid these ads, REGISTER NOW!

KinzeMech

Well-known member
Joined
Jul 15, 2012
Messages
1,164
Flex conduit looks like *** anywhere. Only use it where cosmetic concerns are unimportant.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
X2 with Jason. Also, if you decide to use handy boxes, make sure you also use handy box COVERS in the outlets. Makes for a smoother look!
Handy boxes will almost certainly not be legal. You'll need 4x4 boxes with raised covers for the volume.
 

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
i don't have a code here to reference but if i recall correctly flex has to be supported 12 in from the box and every 4 ft. do not use handy boxes, they are not big enough. you must pull a ground wire.
 

jbberns

Well-known member
Joined
Jan 1, 2012
Messages
105
X2 with Jason. Also, if you decide to use handy boxes, make sure you also use handy box COVERS in the outlets. Makes for a smoother look!


On edit, flex, looks terrible on the outside of drywall...

I've never found Handy boxes very handy!
 