Running multiple circuits through stud (50A and 20A, 6/2 and 12/2)

5mall5nail5

Well-known member
Joined
May 23, 2010
Messages
1,174
Location
Bucks County, PA
Hey guys - so tomorrow I am going to bore the holes through my wooden studs and start running my electrical boxes. I am doing a circuit of 20A and a single receptacle for 50A (using 6/2) 240v outlet. There is a point where the 50A and 20A receptacles will be within the same stud cavity, so there would be like 3 - 4 studs that they would pass through in common.

Is there any code or guidance on passing conductors through the same hole? Can anyone fill me in on this or would it just be better to run them several inches apart in 2 different holes?
 
To avoid these ads, REGISTER NOW!

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
I would drill several holes just because the one hole you would have to drill would be pretty large to get the 6 through and even bigger if it needed to accept additional cable(s).

Limit hole sizes when possible and keep it cleaner by separating the runs would be my advice.

There is no code on this I know of other than no bored holes within 1 1/4" of stud edge or you will have to use nailplates.
 

Joe G.

Well-known member
Joined
Aug 21, 2012
Messages
48
Location
Indiana
He was shooting from the hip and making this up. Not a rule.

True. Just finished new house this summer and know for a fact that it passed multiple inspections with more than one cable per hole in a stud.
 
OP
5

5mall5nail5

Well-known member
Joined
May 23, 2010
Messages
1,174
Location
Bucks County, PA
I read something about the ampacity being decreased if pushing multiple wires through the same hole. I might just play it safe...
 
To avoid these ads, REGISTER NOW!

sparky36000

Well-known member
Joined
Dec 25, 2012
Messages
116
Location
North Dakota
I believe you treat it like conductors in a raceway. More than three current carrying conductors, you have to start derating.
 

bmwpower

Super Moderator
Staff member
Joined
Apr 24, 2005
Messages
12,578
Location
NJ
As a general rule, if they fit in the hole and have room to move, you should be good. Think about all the home run circuits coming to a panel. Does each separate wire have to go through a separate hole? With some panels having 40 circuits, all those holes would exceed the surface area of the top plate.
 
OP
5

5mall5nail5

Well-known member
Joined
May 23, 2010
Messages
1,174
Location
Bucks County, PA
As a general rule, if they fit in the hole and have room to move, you should be good. Think about all the home run circuits coming to a panel. Does each separate wire have to go through a separate hole? With some panels having 40 circuits, all those holes would exceed the surface area of the top plate.

True and I imagine the studs structure would be suspect if it was swiss cheesed with 40 holes lol
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
No, but I needed his signature. Inspector is always right and all that...
Well unfortunately it's mentalities like this that perpetuate power-mad inspectors. If you don't question them once in a while they think they can make up the rules.
He CANNOT deny you his signature if he can't show you the rule in the code book.
 