Running power thru metal

fourjeepin

Well-known member
Joined
Feb 12, 2011
Messages
3,660
Location
Atlanta, GA
In my basement, I am drilling holes thru the beams to pull the power wires thru as they currently drape underneath the structural members. I wondered why al the wires were drilled thru except at these two spots until I looked closely and found a nearly 1/2" plate sandwiched between two oak 2x12s. House was built in 1953. I will be running one 14/2 and one 14/3.

That's the background. Questions are
1 - how big should the hole be? I currently have one side drilled to 11/16 and the other to 1/2.
2 - do I need to do anything to make this be up to code?

Now for the pics! Note the old wiring with the black fabric like covering. It does not have a ground wire and I have been slowly pulling it out and replacing with Romex.
 

Attachments

  • image.jpg
    image.jpg
    131.4 KB · Views: 140
To avoid these ads, REGISTER NOW!
OP
F

fourjeepin

Well-known member
Joined
Feb 12, 2011
Messages
3,660
Location
Atlanta, GA
Can't get more than one image to load at a time. Sorry!

Previous image was view from below. Here is the end view.
 

Attachments

  • image.jpg
    image.jpg
    122.9 KB · Views: 103
OP
F

fourjeepin

Well-known member
Joined
Feb 12, 2011
Messages
3,660
Location
Atlanta, GA
And now the view from straight on. You can see the hole that I have been working on here in this image.
 

Attachments

  • image.jpg
    image.jpg
    142.8 KB · Views: 128

rockwithjason

Well-known member
Joined
Jan 8, 2006
Messages
2,633
Location
Las Vegas
why can you not go around the beam as the original wireman did? personally I wouldn't drill this beam, I would drape it or box it in
 
OP
F

fourjeepin

Well-known member
Joined
Feb 12, 2011
Messages
3,660
Location
Atlanta, GA
why can you not go around the beam as the original wireman did? personally I wouldn't drill this beam, I would drape it or box it in

Good question. Originally they went under as seen in the first picture. Going around is possible, but would have to occur twice as I am running three way switches on either end of this long, narrow room. Your suggestion would add more wire and I am almost done drilling these holes.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
they went around it and didn't drill the beam because it's a code violation to do so. That's a structural beam that's not allowed to be compromised by drilling through it.
 

nolimits76

Well-known member
Joined
Jul 11, 2013
Messages
959
Location
Oklahoma
Granted, we work on bridges, but welding or cutting a beam is a big no-no. As such I would advise against you drilling/torching that beam until you get a professional engineering opinion (in writing) that is okay to do so.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
they went around it and didn't drill the beam because it's a code violation to do so. That's a structural beam that's not allowed to be compromised by drilling through it.

Granted, we work on bridges, but welding or cutting a beam is a big no-no. As such I would advise against you drilling/torching that beam until you get a professional engineering opinion (in writing) that is okay to do so.

X3...

Tommy
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
That little hole in that beam wont mean squat, anyone think this is that closely engineered? But,, any steel with wire passing thru it needs to be grounded.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
Is it that closely engineered that it will structurally fail by drilling a hole? No.
Will there be any issues if a small hole is drilled in the beam? No.
Is doing so an industry accepted practice? Absolutely not.
Is doing so allowed by code? Absolutely not.
Would a building inspector be ok with this? Absolutely not.
With this info, you can make your choices as you see fit, but I know what I would do.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I would bend up some conduit to protect the runs and route around the beam, personally. that's 4 90s but it's still only 14 gauge wire.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Is it that closely engineered that it will structurally fail by drilling a hole? No.
Will there be any issues if a small hole is drilled in the beam? No.
Is doing so an industry accepted practice? Absolutely not.
Is doing so allowed by code? Absolutely not.
Would a building inspector be ok with this? Absolutely not.
With this info, you can make your choices as you see fit, but I know what I would do.

Where did you learn this? Where did some of you learn to do this work?
 
Last edited:

Tyberius

Well-known member
Joined
Nov 26, 2013
Messages
312
Location
Wilmette, IL
I wouldn't drill through any of the beams or joists.

It appears that the ceiling is open, so there is always another way through.

It looks like there are furring strips already on the ceiling, so, I would surface mount emt conduit for the ceiling runs across the joists and put junctions at each end, then fur out to the width of the emt.
 
To avoid these ads, REGISTER NOW!

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
It depends on how it was designed, I'm sure. I highly doubt drilling through to run the wire alone is against any NEC or residential building code.

If it's an engineered product, it would seem that just like an I-joist or anything else the manufacturers would provide instructions which would almost certainly indicate any holes need to be drilled in the middle area and be below a certain size and distance from the edges, and you would be required to follow those instructions. But you'd want to do that anyway.

If it's not engineered and it's from 1953, then I'm not sure what would dictate you couldn't drill through it. Common sense would say make the smallest possible hole in the center to get the wire SAFELY through. Use some thick electrical tape or braided cover to provide physical damage protection from the wire on the edge.

Be very careful when you do the actual drilling. I would drill the wood out using a hole saw to about 1" or more around the hole, then drill in the center of that with your smaller metal bit. Make sure all sawdust is nowhere to be found. It's somewhat easy to start a smoldering fire when drilling metal and wood next to each other.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Agree. It would be totally different if we were talking center span and a hole for a 3 inch drain line but that's the size of a small bolt.
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
Agree. It would be totally different if we were talking center span and a hole for a 3 inch drain line but that's the size of a small bolt.

Nah, plumbers will put a 6" cast iron waste line in a 2x8 joist without blinking an eye :evil:
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Is it that closely engineered that it will structurally fail by drilling a hole? No.
Will there be any issues if a small hole is drilled in the beam? No.
Is doing so an industry accepted practice? Absolutely not.
Is doing so allowed by code? Absolutely not.
Would a building inspector be ok with this? Absolutely not.
With this info, you can make your choices as you see fit, but I know what I would do.
And you can say this with 100% certainty? Using "what you were told" in your 8 years as an electrician many years ago?
Are you now a structural engineer? Building inspector?
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Sorry, I missed the part about it being from before 1953... It's against building code to drill through or cut ANY preengineered structural steel beam without engineering approval. I'm gonna say that the OP's beam wasn't preengineered...

Tommy
 
Last edited:
OP
F

fourjeepin

Well-known member
Joined
Feb 12, 2011
Messages
3,660
Location
Atlanta, GA
Thanks for all of the responses. It is definitely not a pre-engineered beam. It was built on site. I am confident that drilling 3/4" holes will not impact it structurally as it has a few holes already where the 2x12s where bolted to the plate. BTW just to give you an indication of age, the bolts and nuts are square heads.

My concern and reason for posting is making sure this is safe electrically. I am leaning toward inserting some type of plastic/PVC sleeve to make sure live wires never hit the steel plate.

Some other info, wires are run through the 2x12s in many other spots where they is no steel plate sandwich. Also, the ceiling is open. It had a drop ceiling with furring strips, but it was rather rough looking and a lot of it had to come down for new plumbing and electrical to be run on the main level above it. I am leaning towards keeping it open as it is just a man cave, the ceiling aren't that high at only 8' and leaving it open makes it feel less closed in. Once I finish replacing the old non grounded wire and adding some new lights, I will paint the ceiling.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
And you can say this with 100% certainty? Using "what you were told" in your 8 years as an electrician many years ago?
Are you now a structural engineer? Building inspector?

I am neither a building inspector nor structural engineer, leaving me by your estimation wholey unqualified to comment on such topics with only my meager past electrical experience and current electrical engineering experience. I will refrain from commenting on these topics and defer to experts such as yourself.


And since you did provide comment, albiet just an agreement with a previous poster, I have to assume you hold yourself to the same high standards as you hold others and would therefore inquire, which of the 2 acceptable professions are you in the employ of, building inspector or structural engineer?
 

JamieK

Well-known member
Joined
Aug 13, 2009
Messages
1,760
Location
Winston-Salem, NC
Is it an actual I-Beam? Heres what the steel engineers say about it.

http://www.steel-insdag.org/teachingmaterial/chapter28.pdf

Warning - lots of math involved!

As far as actually running the wire though the metal, its done all the time at breaker boxes. Just get one of these to fit the hole.

nWY5e.jpg
 
Last edited:

PugetDude

ALLIANCE MEMBER
Joined
Mar 13, 2013
Messages
22,416
Location
Superstition Mountains, AZ
You've got a flitch beam- these used to be pretty common before enginered lumber came along. It allowed the beam to be shallower and still carry the same load. If you look at the way the floor joists are notched and sitting on a nailed-on ledger board, it's even pre-joist hangar days.

It's definitely not an engineered product, so you can drill through it-and a 1/2"-3/4" " hole isn't going to cause it to sag or fail. As Ishiboo metntioned, you should use sort of bushing to keep the wire from rubbing on the plate. Millions of feet of Romex have been run through metal studs; using a snap-in plastic bushing.

Another way to look at it is to consider what the answers would have been if you posted a picture of the beam with the wires going through a 1/2" hole and asked "Is this 1/2" hole that was drilled in 1953 going to make my house fall down? Of course not- but someone here would have undoubtedly advised you to move out immediately, report the condition to the local building authorities and your insurance company, and hire a structural engineer to analyze the structural integrity of the beam...
 
Last edited: