running power to my garage help.

Corbin5754

Well-known member
Joined
Sep 11, 2016
Messages
47
Location
Indiana
Hi, I want to run a 60 amp sub panel to my outbuilding about 70 ft away from my house (100 amp box) I really only want to run direct burial wiring from house to building, can you tell me what size/type wiring I'll need?
 
To avoid these ads, REGISTER NOW!

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
There are 1000 threads on this....

Not to be rude to a newb, but this is very well covered....each week.

;)

If you have done a search, read other posts, AND have a plan, and want people to give you a critique, I bet you will get more responses.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,019
Location
Modesto, CA
Why do u insist on direct burial?

Conduit is cheap insurance against rocks and future upgrades.

For what u need best bang for the buck is #2 AL MHF.

Dont forget 2 rods and u will need to isolate the neutral bar in the sub which usually means buying a separate ground bar kit.

And yes this topic is covered every week.
 

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
Why do u insist on direct burial?

Conduit is cheap insurance against rocks and future upgrades.

For what u need best bang for the buck is #2 AL MHF.

Dont forget 2 rods and u will need to isolate the neutral bar in the sub which usually means buying a separate ground bar kit.

And yes this topic is covered every week.
It certainly does seem that way. :beer:
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Mobile Home Feeder

And another vote for conduit. Or ditch fill partially with sand and run a warning strip in the ditch. Conduit is probably cheaper.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
#6-3 UF will work for a 60A panel. 6-3 UF is $3+ a foot, Aluminum 2-2-2-4 MHF is about $1.50 a foot plus about $1 a foot for 2" PVC conduit and fittings. In the end it will cost about the same or may be a little less for the #2 MHF with conduit and you'll have capacity up to 90A.

Edit: I should add for the easy to install factor the UF will be the easiest because the only conduit needed is where the wire is exposed to possible damage. MHF needs to be in conduit panel to panel unless you change over to SER at entry to the structure for the inside runs.
 
Last edited:

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
I built my home in 94, same time as a neghbor down the road.

His builder was a 'cheap as ****' builder, and the neighbor is a history teacher- so ZERO questioning, ZERO oversight.

Neighbor had the electrical main fail. Was run under the driveway. Crew dug up the asphalt drive, found the ground smoking- fixed the cable.

2 months later, phone line dead. "Oh well, I guess we will go cellular"

Just last week, his well died. He paid $4500 for an electrician to run 400 ft of (this time) conduit from house to well. #6.

Not a stick of conduit was used for main, telephone or well line.

Most of the homes in this development are 1990s...I expect to hear more and more of direct bury cable failures. Yes, 20 years is way down the road.

Until you get down the road
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,733
Location
NW Iowa
I wouldn't loose any sleep over not using conduit. I rarely use conduit and do not experience many failures unless someone digs into it. There is a lot of direct buried wire around that is 30-40 years old with no issues. When you backfill it is important to make sure there are no sharp rocks within a few inches of the wire. If you have extremely rocky soil then conduit would make sense.

For size of wire a #4 or #2 AL would be fine. Make sure the wire you use is rated for direct burial.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,019
Location
Modesto, CA
I was thinking maybe we wouldn't end up revisiting it if there were a high-quality sticky on it. Lay out the right ways (latest NEC) to do everything from direct-bury single branch up to separate service.

I nominate you to write it. :)

I have already PMd several mods/admins last week with no response.

There is several stickies i would like to collaborate on with several of the other guys on here including pattenp aceman norcal speedy mm etc...

They include difference between EGCs and grounding electrodes

4-wire subpanel

And typical recommendation for feeder to detached garage/shop with one man and nominal loads/equipment.

But i cant get a response from admins so oh well...
 