justinae
Also is 2-2-2-4 Mobile Home Feeder not available in your area? It may be cheaper than buying single THHN/THWN wire. The MHF is already assembled with a white marked neutral and a green ground where as the THHN/THWN you need to mark at the terminations.
Can you run MHF in the conduit? My understanding is that I can run MHF all the way from panel to panel and direct bury in the ground but that there is a risk associated with unprotected cable. I'm not too worried about digging animals but am concerned about some trees that are rooting where my trench is.
pattenp
Virginia - USA
Just make sure the wire you get has the THHN plus THWN rating. The "W" means it's suited for wet locations. Most aluminum wire has what's called compacted conductors. The conduit fill rate it higher for conductors that are compacted. Example is 4 regular stranded #2's will fit in 1 1/4 PVC where as 5 compacted stranded #2's will fit in 1 1/4" PVC conduit.
pattenp
Virginia - USA
Yes MHF can be run in conduit. MHF is rated for direct bury if you don't want to use conduit, but putting it in conduit is a smart thing. MHF has to be in conduit when run inside and it can be run inside because it is fire resistant rated.
J
justinae
OK, THHN with THWN rating and compacted for all stand alone wires.
Thanks, this is really helpful. Now to find the best place to get them. So far Home Despise seems to have the best price for 2-2-2-4 at $1.49/ft.
J
justinae
So what would be the advantage to MHF? If I could run it without conduit in the crawl space and walls then perhaps, but if I need conduit the whole way then SER w/ junction to individual seems easiest.
pattenp
Virginia - USA
There is no real advantage to MHF the whole way other than eliminating a splice, but then you have a lot more conduit to run in the house. MHF has to be in conduit when run inside of the house and garage. SER from the house panel to a junction box and then the MHF to the garage is your other option. Pick your poison.
Except that MHF HAS to be run in conduit when inside a building! I'm not sure why this is cause its fire retardant! @pattenp ???
pattenp
Virginia - USA
MHF has to be in conduit because it is individual conductors and does not have an overall outer jacket. It falls under the same requirement as any single conductor run of needing to be in conduit. If MHF didn't have the fire resistant rating it couldn't be run inside the house even in conduit.
What is the temp grade of MHF? I'm not fully versed on all the different cables out there and have never used this type. Also, the same with SER and SEU. I know they're service entrance cable but I have never run them. I realize this was gone into detail and debated on by you and someone else in another recent thread but I haven't had the time to catch up on all the comments in that thread!
Edit: I've ran SE cables before, just never looked to see if they were SER or SEU!
J
justinae
Very interesting. I think I'll go with individual wire instead of MHF for the short run as it might be easier to fish.
Again, very helpful.
Oh I c. That makes sense. So, this begs the question that if MHF is individual conductors, what's the difference between it and individual wire like THWN? Why is it specifically called MHF other than the obvious?
MHF IS individual wire so there wouldn't be a difference in pulling ease!
I tell ya! I learn something new almost every day!
pattenp
Virginia - USA
To answer your other question about temp on the MHF. It is sized based on 75 degree.
Mobile Home Feeder is a Southwire product and it's their marketing name for the wire product. The main difference from it and individual THHN/THWN is it's an assembled cable and is rated for direct bury and the insulation is rated RHH/RHW-2/USE-2. Southwire's "SIMpull THHN" is a THHN/THWN-2 rated wire.
pattenp
Virginia - USA
Beware some of the 2-2-2-4 Al wire HD sells is URD (Underground Residential Distribution) and is only rated as USE-2. Meaning it cannot be run inside, period. It's not fire resistant.
Falcon67
Merkel, TX
I ran the HD 2-2-2-4 inside and the inspector bought it off just fine. I'd have to look at the wire since I forget exactly what the specs were, but it carried all the proper ratings for that use. It runs 55' through an attic and 36' through 2" conduit. Fused at 70A. Inspected from one end to the other by the local.
pattenp
Virginia - USA
The HD's in Texas probably carry Mobile Home Feeder since Texas is the Mobile Home capital of the US. :lol_hitti
J
justinae
At the store now. The 2 2 2 4 wire says " Alcan s stabiloy aa-8030 Type se cable style r xhhw-2 600v 3 cdrs 2 awg (33.6mm2) 1 cdr 4 awg(21.2) sun-res (ul) 2012"
Is this the right one?
pattenp
Virginia - USA
It's the right cable for the inside. No conduit needed because it's SER.
This is it, right?
pattenp
Virginia - USA
No. I bought a separate #4 for the ground.
Okay. I know what you got. It's Triplex UD. I was thinking Triplex Service Drop. You need to check the insulation markings. I believe it's only rated as USE-2 which means it can't be run inside at all because it's not fire resistant rated. It needs the XHHW or RHH or RHW-2 ratings. I hope I'm wrong.
What's the rating on the #4 ground you bought?
Falcon67
Merkel, TX
Damn straight. Tornado Bait - Got to keep those tornadoes out of New Mexico. :evil: I must confess that at one time we owned a 28x40 on two acres - was a nice place. And damn cheap livin!
I thought u said earlier that MHF is individual conductors? I'm confused! Do u happen to have a pic?
J
justinae
http://www.homedepot.com/Electrical...Id=10053&langId=-1&storeId=10051#.UFFat6RSTUM
That's the triplex I got.
I've been thinking about how to transition from the LB into the garage and see I can get 1 1/4" flex. Then I started thinking that since my run from the junction box to the panel in the garage is only about 10' why not just do it all in flex. Any reason not to? I'll still need the LB but that's it I think. That also makes drilling through the stud easier.
Thanks.
pattenp
Virginia - USA
It is considered individual conductors but is twisted into a cable. Because it doesn't have an outer sheath it is required to be in conduit when used inside.
J
justinae
This may seem like a dumb question, but couldn't I run the SER all the way to the junction and then simply strip off the outer sheathing in the part that runs in the conduit? Then no splicing and much smaller junction box.
I'm not planning to do that, but was just curious.
pattenp
Virginia - USA
Thanks.
I so hate to tell you this but the Triplex you bought is not allowed by code to be used inside of the garage. It is a URD and does not have a fire resistant rating and can only be used outdoors. If you look at the specs on the HD site you'll see that "Fire Retardant" is marked as "No" and "Indoors/outdoors" is marked "outdoors". You can use it but I just wanted you to know it would not pass code.
Norcal
The wire in SER cable is not a recognized conductor outside of the sheathing which this also applies to NM cable, if you look there are no markings on the indv. conductors as to what they are.
J
justinae
I figured it was something like that and that's why it isn't done but was curious anyway. It seems strange that there isn't a more straightforward way to wire a detached garage, but this way isn't too bad.
mrobins297aaa
south east michigan
other than its not to code whats the real risk here?
pattenp
Virginia - USA
Just as Norcal said plus the fact the SER has an uninsulated ground and is not protected from moisture in the conduit so it will oxidize over time.
Ok I see now. We don't have many MHs here so MHF is not something I've run across before!
J
justinae
I have the wire in front of me. It says "Compact Stabiloy AL XLPE 600V USE-2 or RHH or RHW-2"
According to the chart you sent RHH and RHW are both fire retardant.
Am I missing something?
pattenp
Virginia - USA
It's time to celebrate. :beer: You have the correct wire. The HD web link you posted was not the wire you purchased. :lol: It's 1:40AM, I'm going to bed. This has just tired me out.