I understand now.62stepside you maybe confused on the wire sizes and breaker sizes. If the continuous feeder from the source panel to the garage panel is made up of #2/0 and #2 spliced together the source panel breaker feeding the wire to the garage is to be no larger than 90A because of the #2. The subpanel in the garage can have a 100A main breaker because it's a disconnect only and is not the primary breaker protecting the feeder.