Well-known member
Can I run an #18/4 conductor shielded cable (Belden 9418 shielded cable) in the same conduit as some #14 THHN control wires (120 volt)
I know it will work, but is it right?
The #18 4 conductor is using a 4-20mA signal to drive a damper actuator and the #14's are breaking the coil of a contactor thru a switch, if it matters.
everything I see says, you can't mix a class 1 and class 2 circuit, but you can if you treat the class 2 circuit as a class 1 circuit (or something along those lines). The Belden cable is a quality cable and is not designated as a class 2 cable, so I am not sure.
I know it will work, but is it right?
The #18 4 conductor is using a 4-20mA signal to drive a damper actuator and the #14's are breaking the coil of a contactor thru a switch, if it matters.
everything I see says, you can't mix a class 1 and class 2 circuit, but you can if you treat the class 2 circuit as a class 1 circuit (or something along those lines). The Belden cable is a quality cable and is not designated as a class 2 cable, so I am not sure.