Running wire through 4" galvanized steel poles ?

Wizzard

Well-known member
Joined
Jan 28, 2011
Messages
350
I'm using a couple of plain 24ft (4ft in ground) galvanized poles to hang an area light off each pole using direct burial cable. What is the best way to run the electrical wire per NEC? I'd like to go inside the pole, but not sure that is allowed.
 
To avoid these ads, REGISTER NOW!

Keithinsc

Well-known member
Joined
Feb 13, 2011
Messages
1,129
Location
Sandhills of SC
Not sure about an NEC ruling on this, but could you use a weather head to cap the top and be an exit for your wires?
Having wire in the poles shouldn't be any different than if you ran it in conduit.
Traffic poles are set that way all the time.
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
You can go inside the pole, but you need to have a hand-hole at the base of the pole with a weatherproof cover. See NEC 410.30(B).
 
To avoid these ads, REGISTER NOW!

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
On your own property, it's probably fine. If it's somewhere that someone can get hurt when it falls over, I wouldn't do it. Real lighting poles are tested for deflection for wind, vibration and earth movement. Also, they have weight limits for the fixtures that are hung on them. Hanging brackets are made specifically for pole types and sizes.
Be sure to get one that fits.
http://applications.nam.lighting.philips.com/blog/index.php/2012/01/31/what-is-effective-projected-area-epa/
Good luck,
CD
 
OP
W

Wizzard

Well-known member
Joined
Jan 28, 2011
Messages
350
Thanks everyone. I ordered curved 3"x5" handhole covers to retro-fit to the poles. Lights weigh only 18lbs, should be good with a 4" galvanized pole.

From my research it appears it is ok to make my splices inside the pole?
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Splices inside the pole are OK as long as they're readily accessible. In other words, If you remove the handhole cover and the splice is right there behind it, and you can undo/redo the splice just by reaching your hands through the hole, then that's fine. If it's spliced right at the fixture itself, and you can access the splice by simply unbolting the fixture from the pole, then that's fine too. But a splice located halfway up the pole with no real way to access it is not OK.
 