That is why I mentioned a 1x8 or 1x8 board on end to make a small "triangle" that the wires are behind in that space.
Like the green "board" I added in the attached pic.
Chapter 3 Wiring Methods and Materials
Article 334 Nonmetallic-Sheathed Cable: Types NM, NMC, and NMS
334.23 In Accessible Attics. The installation of cable in accessible attics or roof spaces shall also comply with 320.23.
Article 320 Armored Cable: Type AC
320.23 In Accessible Attics. Type AC cables in accessible attics or roof spaces shall be installed as specified in 320.23(A) and (B).
(A) Where Run Across the Top of Floor Joists. Where run across the top of floor joists, or within 2.1 m (7 ft) of floor or floor joists across the face of rafters or studding, in attics and roof spaces that are accessible, the cable shall be protected by substantial guard strips that are at least as high as the cable. Where this space is not accessible by permanent stairs or ladders, protection shall only be required within 1.8 m (6 ft) of the nearest edge of the scuttle hole or attic entrance.
(B) Cable Installed Parallel to Framing Members. Where the cable is installed parallel to the sides of rafters, studs, or floor joists, neither guard strips nor running boards shall be required, and the installation shall also comply with 300.4(D).
I think it boils down to deciding whether or not the area is considered accessible by permanent stairs or ladder.
Based on the fact that there is osb there for walking on, I would say it is but ultimately it's the inspector who will decide.
Don't be afraid to call or better yet, e-mail the inspector assigned to your job.