ryanjharvey
Active member
Hey all - just wanted to post my propane generator setup in hopes it may help a few people when trying to think through the best way to get backup power in their house. Couple of goals I had:
Components utilized:
Thought process behind this setup:
I found a good deal on the generator on craigslist so this was what it was. I knew I wasnt going to run a heat pump furnace or any other 240V loads so a small 120V generator didnt bother me. I'm on city water, dont have a well pump, etc. etc.
Started looking at transfer switches but given my panel is outside, I was going to have to order a 120V Nema 3R outdoor manual transfer switch. These were way more expensive than a generator interlock kit and I didn't see much benefit to this vs manual load selection using the breaker panel.
Another issue I had was that since my gen was 120V, I was only going to get one side of the panel backfed with power. I went ahead and wired my panel for 240V with a 30A/2P breaker from the inlet box and the L14-30R flanged male receptacle, but then utilized an adapter cord that bridges the two hot conductors so that both sides of the panel will have power. Just allows me the option to power what I want, when I want and not have to worry about rearranging breakers.
The inlet box is very well made and seemed to be the best option at the time for what I wanted in an outside receptacle. I DO NOT like the receptacles from reliance and everyone else that just plug in with no hood or in-use device in the front. The Connecticut Electric box has the receptacle on the bottom along with a lid to close it off when not in use. A design that should help against rain in the future.
Here is the setup. Panel is a mess. Hope this helps anyone else thinking about a similar setup.
View media item 56212View media item 56213View media item 56214View media item 56216
- Need a fuel source that storage stable and wont go "bad" from year to year.
- Want the ability to turn on any 120V breaker in my main panel without "deciding" only which loads could be emergency
- Want the cheapest easiest setup that is safe and as code compliant as possible
Components utilized:
- Champion 3500W/2800W 120V propane generator (Champion 76530)
- Square D Homeline Generator Interlock Kit UL Listed (Square D HOMRBGK2C)
- Connecticut Electric 30 Amp Power Inlet Box with Hinged Door and L14-30R male flanged outlet
- Conntek PL530L1430 1.5-Feet Female Locking Adapter for 125-Volt L5-30P Plug to 125/250-Volt L14-30R (Two hots bridged)
- Conntek 20571 Generator Extension Cord 25-Foot 10/3 30 Amp 3 Prong NEMA L5-30 Eextension Cord
Thought process behind this setup:
I found a good deal on the generator on craigslist so this was what it was. I knew I wasnt going to run a heat pump furnace or any other 240V loads so a small 120V generator didnt bother me. I'm on city water, dont have a well pump, etc. etc.
Started looking at transfer switches but given my panel is outside, I was going to have to order a 120V Nema 3R outdoor manual transfer switch. These were way more expensive than a generator interlock kit and I didn't see much benefit to this vs manual load selection using the breaker panel.
Another issue I had was that since my gen was 120V, I was only going to get one side of the panel backfed with power. I went ahead and wired my panel for 240V with a 30A/2P breaker from the inlet box and the L14-30R flanged male receptacle, but then utilized an adapter cord that bridges the two hot conductors so that both sides of the panel will have power. Just allows me the option to power what I want, when I want and not have to worry about rearranging breakers.
The inlet box is very well made and seemed to be the best option at the time for what I wanted in an outside receptacle. I DO NOT like the receptacles from reliance and everyone else that just plug in with no hood or in-use device in the front. The Connecticut Electric box has the receptacle on the bottom along with a lid to close it off when not in use. A design that should help against rain in the future.
Here is the setup. Panel is a mess. Hope this helps anyone else thinking about a similar setup.
View media item 56212View media item 56213View media item 56214View media item 56216