Are there any code requirements as to the placement of safety switches - have to be within so many feet of the appliance?

I'm looking to replace the safety switch for the well pump. Thought about just mounting it right next to the switch for the water heater for convenience sake. That would put the safety switch about 16 feet from the actual well.
 
To avoid these ads, REGISTER NOW!

malibu101

Well-known member
Joined
Jul 1, 2005
Messages
3,910
Location
Walnutport PA
I don't know the exact NEC code section number-
But the disconnect must be within sight of and less than 50' away from the equipment it is disconnecting.
 
To avoid these ads, REGISTER NOW!

'04 Cummins

Well-known member
Joined
Jul 14, 2012
Messages
137
Location
MD
If the safety switch can be locked out, it doesn't have to be within sight of the equipment.
 