Sanborn 60 gallon wiring
tedo2007
Just wanting to make sure I buy the right wire and breaker for the box what should I get?
T
tedo2007
Can I get away with 10-2? How about a 20 breaker? I have both.
The gallon rating means nothing for circuit wiring.
Its the motor HP rating that determines the circuit size.
So 3HP motor needs #12 THWN in pipe or 10/2 NM-b.
A 20a breaker may or may not hold. If it nuissance trips, you can use a 30a.
You will also need a disconnect if the comp is not within sight of and further than 50' away from the breaker panel.
T
tedo2007
Yessir that’s why I posted the pictures for the amp rating. Thanks for your help!
sberry
Brethren, Michigan
The 6-50 wouldnt bother me, if you have the 10 wire go for it. Modern breakers are pretty sturdy, it might work on a 20,, worse thing it trips, if I had a 30 wouldnt be scared to use it especially with a heavy wire. Not really for the wire but trips, good service and big wire lesss them really pull on starts especially if they are close to the source.
Bert_
NW Iowa
30a breaker is the same price or sometimes even cheaper that a 20. Why put a marginal sized breaker in? Code would allow up to a 40 maybe even 50a breaker.
30A breaker would be my choice.
sberry
Brethren, Michigan
My well is 3 hp. A 20 worked for about 10 years, then every once in a while, once a year or so would trip. Not sure if it was breaker or equipment but hasnt done it with 10 more yrs on a 30.
I see a couple well instalations with fuses,, 12 wire with 30.
T
tedo2007
I could snag a bigger breaker and or wire also if needed just figured this makes sense
Bert_
NW Iowa
#12 thhn or #10 Romex can be used with any of the breaker sized listed in a motor circuit.
3HP well? That must be a deep well.
Bert_
NW Iowa
Not necessarily depth but also flow.
2-3hp isn't really uncommon. A lot of hog buildings have pumps this size.
Biggest private well pump I've wired on was 15hp at a big feed lot, had two of them. Back when they were run by pressure switch and starters they used an old railroad tanker for a pressure tank. 5 years ago or so they got VFD's and pressure transducers. Now they use a 60 gallon or so pressure tank. I think the water line comming out of the well casing is 2-3?"
sberry
Brethren, Michigan
Its 320 with pump at 220 or so and makes close to 35 gpm. I have a 301 or 351 well x trol tank on it. 1 1/4 pipe on it, they actually used 1 1/2 coming up hole.