Just wanting to make sure I buy the right wire and breaker for the box what should I get?

2f4a5b873b41e38837e700c4c518946c.jpg

164cf215c8c995508ab9094e00d73c27.jpg


Sent from my iPhone using Tapatalk
 

Attachments

  • 2f4a5b873b41e38837e700c4c518946c.jpg
    2f4a5b873b41e38837e700c4c518946c.jpg
    530.5 KB · Views: 0
  • 164cf215c8c995508ab9094e00d73c27.jpg
    164cf215c8c995508ab9094e00d73c27.jpg
    513.6 KB · Views: 0
To avoid these ads, REGISTER NOW!
OP
T

tedo2007

Well-known member
Joined
May 19, 2014
Messages
104
Can I get away with 10-2? How about a 20 breaker? I have both.


Sent from my iPhone using Tapatalk
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
The gallon rating means nothing for circuit wiring.

Its the motor HP rating that determines the circuit size.

So 3HP motor needs #12 THWN in pipe or 10/2 NM-b.

A 20a breaker may or may not hold. If it nuissance trips, you can use a 30a.

You will also need a disconnect if the comp is not within sight of and further than 50' away from the breaker panel.
 
OP
T

tedo2007

Well-known member
Joined
May 19, 2014
Messages
104
Yessir that’s why I posted the pictures for the amp rating. Thanks for your help!


Sent from my iPhone using Tapatalk
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The 6-50 wouldnt bother me, if you have the 10 wire go for it. Modern breakers are pretty sturdy, it might work on a 20,, worse thing it trips, if I had a 30 wouldnt be scared to use it especially with a heavy wire. Not really for the wire but trips, good service and big wire lesss them really pull on starts especially if they are close to the source.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,758
Location
NW Iowa
30a breaker is the same price or sometimes even cheaper that a 20. Why put a marginal sized breaker in? Code would allow up to a 40 maybe even 50a breaker.

30A breaker would be my choice.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
My well is 3 hp. A 20 worked for about 10 years, then every once in a while, once a year or so would trip. Not sure if it was breaker or equipment but hasnt done it with 10 more yrs on a 30.
I see a couple well instalations with fuses,, 12 wire with 30.
 
OP
T

tedo2007

Well-known member
Joined
May 19, 2014
Messages
104
I could snag a bigger breaker and or wire also if needed just figured this makes sense


Sent from my iPhone using Tapatalk
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,758
Location
NW Iowa
I could snag a bigger breaker and or wire also if needed just figured this makes sense


Sent from my iPhone using Tapatalk

#12 thhn or #10 Romex can be used with any of the breaker sized listed in a motor circuit.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
My well is 3 hp. A 20 worked for about 10 years, then every once in a while, once a year or so would trip. Not sure if it was breaker or equipment but hasnt done it with 10 more yrs on a 30.
I see a couple well instalations with fuses,, 12 wire with 30.

3HP well? That must be a deep well.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,758
Location
NW Iowa
3HP well? That must be a deep well.


Not necessarily depth but also flow.

2-3hp isn't really uncommon. A lot of hog buildings have pumps this size.

Biggest private well pump I've wired on was 15hp at a big feed lot, had two of them. Back when they were run by pressure switch and starters they used an old railroad tanker for a pressure tank. 5 years ago or so they got VFD's and pressure transducers. Now they use a 60 gallon or so pressure tank. I think the water line comming out of the well casing is 2-3?"
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Its 320 with pump at 220 or so and makes close to 35 gpm. I have a 301 or 351 well x trol tank on it. 1 1/4 pipe on it, they actually used 1 1/2 coming up hole.
 