Sanity check on Sub-Panel wiring

Dal Bone

Active member
Joined
Feb 11, 2016
Messages
25
I have never wired a sub-panel before and looking for a sanity check.

When I finished my basement I had the contractor install a 50 amp breaker in my main panel and I ran 6 gauge wiring up into my garage.

In the panel I have 2 20amp circuits for additional outlets and 1 20 amp circuit for a dedicated dust collector.

I also have 2 30 amp circuits for future expansion for either tools for an EV charger.

How is everything looking?
 

Attachments

  • IMG_4928.jpeg
    IMG_4928.jpeg
    616.8 KB · Views: 131
  • IMG_4927.jpeg
    IMG_4927.jpeg
    744.2 KB · Views: 129
  • IMG_4925.jpeg
    IMG_4925.jpeg
    640.5 KB · Views: 131
To avoid these ads, REGISTER NOW!

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
First pass, the green screw likely needs to be entirely removed, for a sub panel. It ties the ground and neutral together which is only for the main panel and should not be done on a sub (so remove it).

You may want to note your location as codes are not the same everywhere....
 
Last edited:

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I'm assuming this is an attached garage, yes? If so, everything looks good, except I would also completely remove the bonding screw.
 
OP
D

Dal Bone

Active member
Joined
Feb 11, 2016
Messages
25
Yes attached garage. I am located in Utah.

Thanks for the heads up on the bonding screw. I seem to remember reading that instruction but must have forgot.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,803
Location
VT
Where are you grounds landed?

Edit: I see it. I would move all your connections from the feed along the right hand of the panel, would be cleaner
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,011
Location
Modesto, CA
other than the aforementioned bonding screw removal, and i cant tell if you terminated the EGC on the left bar, its a bit messy.

The NM you have coming in on the upper right circles the can and terminates on the same side so you have all that slack.

same for the feeder conductors

I would remove it all and cut down on the slack. run the branch circuit conductors straight down to the breakers and bus bars on the same side of the panel

same for the feeder. bring them up one side and terminate them.

as you add circuits down the road youll appreciate not having all that slack in there
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
There should be an insulating bushing on the conduit end where the feeder enters.
Edit: I see that's a NM clamp not conduit so a bushing is not needed.
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,802
Location
Southern Oregon
Should have installed the panel with the feed lugs on the bottom. Too late now.

Trim up the NM jackets, especially on the feeder. Just looks sloppy with the extra jacket and paper hanging out. You need 1/4" minimum of jacket.
 

Tundra1

Well-known member
Joined
Sep 3, 2023
Messages
201
A lot of the guy's I work with clean up their tray cable sheathing trim point with a piece of shrink tube. So the conductors exit the sheathing in a tidy look, even inside panels. Is this ever done or allowed with NM?
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,953
Location
Coronado, CA
With the of the comments about neatness and removing the bonding screw, I am going to say it looks OK to me.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,011
Location
Modesto, CA
A lot of the guy's I work with clean up their tray cable sheathing trim point with a piece of shrink tube. So the conductors exit the sheathing in a tidy look, even inside panels. Is this ever done or allowed with NM?
No not ever done and theres no point.

For tray cable i can see a point
 

Tundra1

Well-known member
Joined
Sep 3, 2023
Messages
201
Thanks. I've never seen it either on nm, just gives a nice polished look.
 