The data plate on the motor is

model C-140-3013
5KCR48SR59W
RPM 3450
V 230
A 13.1
Code 839M
PC B1037
40C AMB CL

It is on s sears 5hp air compressor. The plug on the compressor is for a nema 6-20.

Do i then need a 20 amp breaker?

I currently have a 30 amp breaker 10 gauge wire 240v hooked up to a 200amp service panel running to the location where I would like to have the air compressor. Can I install a nema 6-20 oulet on this run?
 
Last edited:
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,096
Location
Modesto, CA
Thats not a true 5HP motor. Amps are too low.

Its more like a 2 or 3HP motor.

Nema 6-20p will be fine with #12 wire. Breaker needs to be 20a.

Motor circuit wiring is sized @ 125% of NEC FLC.

Breaker can be max 250% of NEC FLC.

EDIT: I really shouldnt type up technical comments when Im half awake. If u use a 6-20P and r, then the breaker needs to be 20a.
 
Last edited:
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
Is it ok if in install a Nema 6-20 outlet on a 30amp breaker?
 

md21722

Well-known member
Joined
Nov 30, 2015
Messages
1,840
Location
Mt Juliet, TN
Yeah, I just realized we were talking breakers vs outlets so I deleted my message before even seeing your response :)
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Thats not a true 5HP motor. Amps are too low.

Its more like a 2 or 3HP motor.

Nema 6-20p will be fine with #12 wire. Breaker can be 20a or 30a.

Motor circuit wiring is sized @ 125% of NEC FLC.

Breaker can be max 250% of NEC FLC.

That's okay for a hardwired motor circuit, but not a circuit with an outlet.

Read NEC 430.42(C).
 
Last edited:
To avoid these ads, REGISTER NOW!

Gttrucker

Well-known member
Joined
Sep 2, 2016
Messages
53
Wyleisdeisels is correct. That is not a true 5hp. If I recall correctly 1 HP equals about 750 watts, so 5 HP is 3750 watts. At 230 that's 16amps.
So your fine with 12 gauge line and 20 amp connectors even if it was a true 5hp. I always wonder how they come up with HP ratings on motors. Air compressors are always over rating their power to sell their stuff.

A note on the cord. I see a similar problem with extension cords. They often have more resistance than the rated gauge should have, so if your planning to buy a coed and cut the end off (as opposed to just buying cable) then I'd get a 10 gauge cord 'cuz I don't trust their numbers.
 

Gttrucker

Well-known member
Joined
Sep 2, 2016
Messages
53
If this is a stationary compressor you could just skip the plugs and cable and hard wire it direct with 12/3 armored cable. It's fairly cheap and handy to have on hand for running extra outlets etc.
 
Last edited:

Gttrucker

Well-known member
Joined
Sep 2, 2016
Messages
53
pattenp is right. A true 5hp should have a 30amp/10ga line ... hmmm but this is not really a 5hp motor it's a 13amp motor so 12/3 should be fine.
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
pattenp is right. A true 5hp should have a 30amp/10ga line ... hmmm but this is not really a 5hp motor it's a 13amp motor so 12/3 should be fine.

I currently have a 30amp/19 gauge line going to the location. If I put the 20gauge outlet on the line and only used it to connect the air compressor would that be ok?

Thanks for the help
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I currently have a 30amp/19 gauge line going to the location. If I put the 20gauge outlet on the line and only used it to connect the air compressor would that be ok?

Thanks for the help

If you have #10 wire you can use a 20 amp breaker and a 20 amp outlet. It's going to be tough connecting #10 to a 20A outlet and getting it all back into a standard single box if that's what you have. You should not use a 30A breaker.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,096
Location
Modesto, CA
I currently have a 30amp/19 gauge line going to the location. If I put the 20gauge outlet on the line and only used it to connect the air compressor would that be ok?

Thanks for the help

19 gauge wire? :wtf: Thats really small.

I hope u meant 10 gauge...
 