Separated Combustion Garage Heater

meinckdp

New member
Joined
Feb 19, 2021
Messages
3
Location
Wisconsin
I'm looking into installing a ceiling hung natural gas heater in my garage, but am new to heaters and still learning. I like the idea of separated combustion and not having to worry about saw dust or fumes being a problem, but having to run a condensate drain line will be an issue. I don't have a drain in my garage to run a line to and there is no easy way to run a condensate line back to the house. Is there such thing as a separated combustion heater that you wouldn't need to run a condensate drain line on? I had trouble looking it up elsewhere.
 
Last edited:
To avoid these ads, REGISTER NOW!

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,047
what unit are you looking into? an 80% won't have a condensate line. a condensing will, and you have to keep a set temp over freezing.
 

Steve in UT

Well-known member
Joined
Oct 30, 2018
Messages
205
Location
....
Stick a hose/pipe out the wall with some heat tape on it. Run it into a bucket/barrel and dump when needed (install a full alarm.) Knock a hole in the floor and dig a few feet into the dirt and let the ground soak it up. Just a few ideas off the top of my head.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
There will condensation ( small amount) either way........tip the exhaust slightly downward contrary to the instructions.* Allows the water to drip outside vs staying in pipe or worse back into the heater. They all drip some. My radon vent drips with just air venting not heated combustion exhaust. It will cause a similar ice sculpture as the picture.

Garage heater exhaust-
5C5C4C9F-5E00-4CA3-9CB3-71A4190C1B0C.jpg


* some instructions say tip back towards the heater, seems wrong, suppose some might tip exhaust several inches downward which might cause a problem in venting. Water just needs 1/8-1/4” down over the exposed pipe.

Some instructions say the drain on 80% furnace horizontal vent is only required on commercial applications.


There is point where if sealed combustion is required or highly desired 90plus furnace makes sense. But that amplifies the condensation drain issue.

There’s as the other side where fresh air intake in garage heater is not that important.
 
Last edited:

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
What size is the garage ? Do you have NG

They are a bit more money ..but, I love my cabinet heater. They are only 80% no drain.

Nice thing about them is they are bit quieter -- they come with everything (vent). They use a single hole in the wall for the intake and exhaust. Easy install .. sealed combustion. The better ones are modulating ... really nice.

I think code would want at 18" -- they put the heat at the floor where it should be
 
OP
M

meinckdp

New member
Joined
Feb 19, 2021
Messages
3
Location
Wisconsin
what unit are you looking into? an 80% won't have a condensate line. a condensing will, and you have to keep a set temp over freezing.

I was planning on keeping the garage at 50 degrees. I've been looking into the Sterling GG75 heater, the Modine Hot Dawg 75 (not sure between the HDC or HDS model) and a Reznor.
 
OP
M

meinckdp

New member
Joined
Feb 19, 2021
Messages
3
Location
Wisconsin
What size is the garage ? Do you have NG

They are a bit more money ..but, I love my cabinet heater. They are only 80% no drain.

Nice thing about them is they are bit quieter -- they come with everything (vent). They use a single hole in the wall for the intake and exhaust. Easy install .. sealed combustion. The better ones are modulating ... really nice.

I think code would want at 18" -- they put the heat at the floor where it should be

Garage is approximately 32 x 22. I do have natural gas. Which cabinet heater do you have?
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Garage is approximately 32 x 22. I do have natural gas. Which cabinet heater do you have?

Have an Empire -- the new Rinnai will modulate.

I'm talking about the sealed models -- not the vent free.

Have you done a heat load on the space? At only 750sf -- if you have it reasonably insulated and a decent door ... with NG .. the cost to heat may surprise you .

I can heat my whole 1700sf studio with a 38/40 80% unit when 0 out in PA -- I keep it in the low 60's .. and I have propane!. Unless you are on a really tight budget my guess plan on higher than 50.
 

TurnipTruck

Well-known member
Joined
Aug 28, 2005
Messages
1,551
Location
Southcentral Alaska
I just hung an 80kbtu separated combustion heater (big maxx?) with the flue sloped down so any condensation drips outside. My shop is sealed pretty tightly (as tight as it can be with three overhead doors) and I wanted to control the infiltration air. Any modern common heater with intermittent pilot has an exhaust blower, so a rising flue is no longer necessary as it would be with a standing pilot.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,047
I've never seen condensation on an 80% exhaust, even in crazy weather. my guess is too much pipe outside allowing it to condense in the pipe.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I just hung an 80kbtu separated combustion heater (big maxx?) with the flue sloped down so any condensation drips outside. My shop is sealed pretty tightly (as tight as it can be with three overhead doors) and I wanted to control the infiltration air. Any modern common heater with intermittent pilot has an exhaust blower, so a rising flue is no longer necessary as it would be with a standing pilot.

That's not the case -- you have to follow the manufacturers direction.
 

thammel

Well-known member
Joined
Oct 3, 2005
Messages
2,236
Location
Maryland
I have a reznor udas and as all say, the pipes are slightly sloped to the exterior. There is no need for a condensate line.
 
To avoid these ads, REGISTER NOW!

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,406
Location
N CA
;) All the Rinnai Direct Vent units have modulated since ‘91. All vents will condense at times. It is called the “wet time”. The goal is to limit the wt that each vent sees. This is accomplished with insulated pipe and limits on length of run, rise, etc, and material choice. If I was seeing condensation in an 80%’er I’d want to know how much of it is being produced, meaning trap the line and run it to a bucket. Flue gas condensation runs about 3.2 on a pH scale and is corrosive so keep it out of the HX. I have seen systems where people drill a hole through the slab to drain the condensate. It might work in Indiana where you have a Lime base soil, but in New England I saw a house that the owner stepped on his basement floor one day an the floor broke out below him. Concrete is a lime based product and the 3.2 water ate the slab from below. Substantial amounts of condensate should be neutralized. They make small neutralizer kits and you just have to replace the limestone chips.
 

thammel

Well-known member
Joined
Oct 3, 2005
Messages
2,236
Location
Maryland
Also....with my Reznor UDAS, all pipes leading to the exterior (horizontal runs - intake and exhaust) are type 3 stainless steel, so rust is not an issue.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Keep in mind, fuel burning condensing appliances have to have a condensate neutralizer, regardless of where it drains to. Many locations also require it to drain to an "approved" waste receptacle or sewer line.

Tommy
 
Last edited:

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Also....with my Reznor UDAS, all pipes leading to the exterior (horizontal runs - intake and exhaust) are type 3 stainless steel, so rust is not an issue.

CAT III stainless exhaust has been required on all horizontal vents of garage style heaters for several years.
 

cleanspg

Well-known member
Joined
Nov 5, 2014
Messages
52
I have a Sterling GG with separated combustion. 80% + efficiency and no separate condensate line.
The instructions show how to setup the exhaust. Stainless is required.

For a horizontal vent it has to slope to the outside and it does drip a lot. This last week created a two foot tall icicle on the ground outside.

For a vertical vent any horizontal portion needs to slope back to the heater so that you don't have a place for condensation to collect in your exhaust.

Get the manuals for the heaters you are looking at, and look at the recommended installation. All the info is there and could be different depending on the model. Likely any 80% efficiency model will be the same or similar as what I have described.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
I have a Sterling GG with separated combustion. 80% + efficiency and no separate condensate line.
The instructions show how to setup the exhaust. Stainless is required.

For a horizontal vent it has to slope to the outside and it does drip a lot. This last week created a two foot tall icicle on the ground outside.

For a vertical vent any horizontal portion needs to slope back to the heater so that you don't have a place for condensation to collect in your exhaust.

Get the manuals for the heaters you are looking at, and look at the recommended installation. All the info is there and could be different depending on the model. Likely any 80% efficiency model will be the same or similar as what I have described.

The condensate line is for those that are designed to condense -- they have the secondary heat exchanger. The main flue has to follow the instructions -- the manufacturers test the equipment and they have to factor in the "what if"
 

cleanspg

Well-known member
Joined
Nov 5, 2014
Messages
52
The condensate line is for those that are designed to condense -- they have the secondary heat exchanger. The main flue has to follow the instructions -- the manufacturers test the equipment and they have to factor in the "what if"

Got it. As I under stand it the secondary heat exchanger pulls more heat out of the exhaust creating a condition where you will always have condensation because of the colder exhaust and this is how you get to 90%+ efficiency.

My main point was that I don't know of any 90% efficiency garage unit heaters and if the ones he is looking at are in the 80% range, he will not have to deal with a separate condensate line as it won't have one. Condensation in the flue is an issue at 80% and it is dealt with by following the manufacturers directions for installation.

I believe this was the original issue being discussed. You can't just drain a condensate line to the outside as it might freeze and back up and draining it on your slab is a no go etc. It requires in most cases an internal drain to send it down. None of this should be an issue because the heaters he is looking at will not have one.

Separated combustion != condensing.

I assume the confusion comes in because most "normal" furnaces that are set up for separated combustion are 90% + efficiency and will have a condensate line.
 

danski0224

Well-known member
Joined
Jan 29, 2005
Messages
13,346
Location
Near Naperville, IL
I'm looking into installing a ceiling hung natural gas heater in my garage, but am new to heaters and still learning. I like the idea of separated combustion and not having to worry about saw dust or fumes being a problem, but having to run a condensate drain line will be an issue. I don't have a drain in my garage to run a line to and there is no easy way to run a condensate line back to the house. Is there such thing as a separated combustion heater that you wouldn't need to run a condensate drain line on? I had trouble looking it up elsewhere.

Yes, there are "separated combustion" unit heaters with an 80% AFUE rating. These do not create condensate.

Some heater manufacturers have a "residential" line of unit heaters, and these separated combustion heaters might be listed with the commercial equipment.
 

cadunkle

Well-known member
Joined
Feb 13, 2011
Messages
472
Location
NJ
No condensate line on Sterling GG heater. I have a 45k unit and it has worked well for me. Currently venting through vertical B-vent as it was already there when I got the place, from a previous repurposed house furnace.

Supposedly if I run the intake outside for separated combustion it's worth another 3% efficiency. Any savings would be trivial as it only costs about $.59/hr to run full tilt, an hour to get to temp then cycles maybe a couple times per hour. It not pulling air from inside might make it a bit more comfortable from not pulling cold outside air into the heated space, and of course has the benefit of greatly reduced risk of incident if it ever gets particularly flammable inside. I may change it to separated combustion eventually.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Burning NG or Propane produces lots of CO2 and H2O -- with 85% equipment the heat of the burn is enough to take the H2O up and out. Sealed combustion does have the "help" of a fan typically .... there were old units that just had intakes (so it can get confusing)

Also -- sealed combustion is not the same as having no flame exposed (explosion proof)

Once you start to go above the 85% -- the only way to get this extra efficiency is to try and capture the heat that you would otherwise allow to go up the flue. The flue gas is allowed to cycle around a second heat exchanger ... before it goes outside. When the flue gas is in this second heat exchanger -- it is cooled ..normally by the air coming back from the room ...or returning water in a boiler. This air or water is now warmer than it would otherwise be as it enters the main heat exchanger. More heat out of the fuel. This lower temp cools the flue gas --- lots of water comes out of this exhaust. Condensation ..... it has to go someplace. Normally gravity or a pump.

with 85% equipment -- if the flue is too long or pitched incorrectly .... the lines can drip. Most equipment is designed to take a bit a water .... this will happen on cold start ... but once the flue heats up .. this water quickly evaporates.

High efficiency equipment still has lots of water in the flue .... anyone with a 96% will still see lots of moisture on a cold calm day coming out of the pipe. That's your 4%

With a boiler -- the key is to get that return water low ... that's why radiant works so well with high efficiency boilers. Cool water coming back -- cool secondary heat exchanger. If you have high temp water coming back = no condensing. That's why you don't typically get all the savings when you have baseboard with a wall boiler.
 

iowa27

New member
Joined
May 22, 2021
Messages
4
Interested in this thread. I bought a Modine separated combustion and want to vent it vertically. I'm a DIYer but need some advice on correct venting supplies. Cat 1, Cat 3, stainless steel, etc ?

Also, I've looked all over the web but haven't found a good illustration of what I'm trying to do. I will be blowing cellulose insulation and wondering about how close the insulation can be against the exhaust vent.
Thanks in advance for any advice
 