Hey fellas - I have a question regarding feeder cables for a sub-panel. 3 paragraphs below is the background, and then my main questions are at the bottom:
Even with tandems and quads I’m running out of space in my main shop panel, so I’m planning to put in a 125A sub-panel inside the building located nearby the main. The 400A main on the shop is surface mounted to the exterior of the building (standard practice for stucco buildings here in AZ).
I would power the subpanel from a 125A breaker in the main panel, and locate the new sub-panel inside the shop, about 1-2 stud bays over from where the wires of the main panel pass through the wall from the exterior. It will be flush mounted between studs. Both the 125A breaker and subpanel are rated for AL conductors.
The feeders will run from the 125A breaker inside the exterior 400A panel down to a knockout at the bottom rear side of the 400A panel (below the bus bars), through the wall into a stud bay and over 1-2 stud bays and up into the 125A sub-panel. Note that the stud bays will be insulated. I realize the bend radius of the feeders is probably going to be my biggest challenge. I’m estimating the total run to be under 8 feet.
Questions:
I would still be interested in protecting the feeders inside the wall, but seems like rigid conduit would be a nightmare for something like this. The last thing I want to do is run a nail/screw into these feeders.
Even with tandems and quads I’m running out of space in my main shop panel, so I’m planning to put in a 125A sub-panel inside the building located nearby the main. The 400A main on the shop is surface mounted to the exterior of the building (standard practice for stucco buildings here in AZ).
I would power the subpanel from a 125A breaker in the main panel, and locate the new sub-panel inside the shop, about 1-2 stud bays over from where the wires of the main panel pass through the wall from the exterior. It will be flush mounted between studs. Both the 125A breaker and subpanel are rated for AL conductors.
The feeders will run from the 125A breaker inside the exterior 400A panel down to a knockout at the bottom rear side of the 400A panel (below the bus bars), through the wall into a stud bay and over 1-2 stud bays and up into the 125A sub-panel. Note that the stud bays will be insulated. I realize the bend radius of the feeders is probably going to be my biggest challenge. I’m estimating the total run to be under 8 feet.
Questions:
- Is SER most appropriate for this application, or is there a better alternative that may have a tighter bend radius and easier to work with? (I was planning on Aluminum 2/0 4-wire SER)
- Does SER require conduit in this situation?
- Given that 2/0 SER is about 1-1/8” OD, what is the best way to attach it along studs/blocking?
I would still be interested in protecting the feeders inside the wall, but seems like rigid conduit would be a nightmare for something like this. The last thing I want to do is run a nail/screw into these feeders.