Service drop amps

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
I need to know how many amps my service can supply. Im not confident that my main breakers reflect that.

Ive asked the power company several times. They wont tell me.

Id rather not hire another electrician (yet).

Tks,
Paul
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
We're going to need a little more information. What is the size of the main? The wire? Overhead or underground? Post pictures.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,940
Location
Rhode Island
Something to keep in mind is that the power companies have their own system they use to determine wire size, not the NEC sizing guidelines that you have to use inside your house. The wire coming from your pole will be way smaller than the wire allowed in your home.

A local lineman told me that the triplex wire coming from the pole will typically be 2 or 4 AWG aluminum.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
definitely need more details here. how about a few pictures of the main service panel, the main breaker, the meter, the inside of the panel with the cover off (if youre comfortable)...

BTW why do you need this info?
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
It's gonna be lot more amps than any panel you can buy for residential. Even if you double tap the mains for another large panel. Within reason and to code, of course.

So how many panels are you thinking?
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
What is your service agreement with your service provider? They should be able to tell you whether you have a 100 or 200 Amp service for example.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,708
Location
NW Iowa
I'm not even sure what the question is. Even if I knew the question there isn't enough information to answer it
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,708
Location
NW Iowa
On the utility side they don't really care what size your main breaker is. They size stuff to the actual load. They know a residential 200A service will use less than 60A 99% of the time.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
did you miss the part about him already talking to them and they wouldnt tell him?
It is an essential component of rate structure. The customer is entitled to know what it is he is paying for. Same as knowing the data rate provided by your internet ISP. Not providing the information is asking for PUC intervention.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
If the OP were to post detailed photos we could figure things out, as it is this thread is on a continuous loop.
 
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
websites think its so cool now to include some contact from links posted, even though some ppl might think what they see is all there is and therefore not click the link. unless I make a point of saying there are 5 pics there. still some ppl dont. its happened several times when Im posting on automotive & plumbing forums. Done venting.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,940
Location
Rhode Island
Just attach the pictures directly to the forum. It's easier, and we'll have the images forever.

I'm confused as to what you are trying to show us.

Are you trying to show us the wires coming from the pole, or the wires going into your service entrance? The wires coming from the pole are probably 2 or 4 AWG aluminum. Undersized by the NEC, but the power company doesn't have to follow NEC rules. Since the wires are in open air, they don't really worry about them getting hot and potentially burning something. The power company will only replace those wires if you have excessive voltage drops.

If you're talking about the wires going into your service entrance/weather head (since you took a close up picture of them) - those are you wires - you own those. You can check what size they are down in your panel. It will be printed on the cable.
 
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
those wires dont go to my panel, they go to meter. I have no access to meter rear. only access is to remove meter.

I need to know if both sets of wires (mine and theirs) can handle 200a.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,584
Location
BC
Check the meter base for an amp rating or model (and Google the specs). They are typically 100A or 200A rated.

The wire in and out of the meter is normally the same size.... unless the installer was using up scraps.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,708
Location
NW Iowa
What size main do you have now? Based on the pics I would guess 150A. 1/0-2/0 wire in the service mast. #4 or #2 from the street.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,940
Location
Rhode Island
those wires dont go to my panel, they go to meter. I have no access to meter rear. only access is to remove meter.

I need to know if both sets of wires (mine and theirs) can handle 200a.
You own those wires, too. They should be the same size wires going into your panel.

Don't worry about the wires coming from the pole. They will not change those wires unless you have a problem (i.e, severe voltage drop).
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
It is an essential component of rate structure. The customer is entitled to know what it is he is paying for. Same as knowing the data rate provided by your internet ISP. Not providing the information is asking for PUC intervention.
huh? maybe in your area but in mine we are not charged based on the size of our service. it isnt even listed on our bill.... and comparing that to internet service speed is a flawed comparison

BTW when i lived in a different part of california and had Profit, Gouge, & Execute, they didnt charge based on size of service nor did they list the size of my service on my bills.
 
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
"What size main do you have now? Based on the pics I would guess 150A. 1/0-2/0 wire in the service mast. #4 or #2 from the street." The quote button does nothing at my end.

Two ele panels, both have 100 main. Each hooks to it's own power meter with 4awg. The service drop supplies both.
 
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
penny is held next to wire, so size shows proportional.
 

Attachments

  • IMG_20230718_180008671.jpg
    IMG_20230718_180008671.jpg
    829 KB · Views: 49

bronc076

Well-known member
Joined
Jul 17, 2023
Messages
190
Location
Ozarks
Instead of guessing at capability of your current service let's discuss your future requirement. What are you trying to achieve? How many amps do you want?

See the CL 200 on the meter pic, that's a 200 amp meter.

Remember your main breaker like all breakers only reflects capability down stream. The role of the main is to protect the panel, just like each breaker protects the wires it provides power to.

You could turn everything on, get an amp clamp and go up there and see what you are drawing, but that still won't answer your initial question.

My service capacity is on my bill but as stated by others that's not always the case.
 

Attachments

  • IMG_5367.jpeg
    IMG_5367.jpeg
    587.4 KB · Views: 45
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
"Two ele panels, both have 100 main. Each hooks to it's own power meter with 4awg. The service drop supplies both." So i need that SD and meter drop to be able to supply 200.

Doesn't main breakers also effectively protect the SD and meter drop?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
I am at a loss as to what the question really is, but I'm going to guess that it's "What size service do I have?" Post #23 states there are two 100 amp panels with #4 service entrance to individual meters. It's a 200 amp service. You can't base it on the POCO wires, they can do whatever they want, and in free air, wires can handle a helluva lot more current than if they are in conduit or buried. The conductors in the mast look like they are at least a 2/0 and if those are copper are what a 200 amp residential service uses. It's fine.

And the POCO doesn't care about what's in the mast, those are your wires. If you really, really need to know exactly what you have, you're going to have to call an electrical contractor and pay them to come look at it.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
"Two ele panels, both have 100 main. Each hooks to it's own power meter with 4awg. The service drop supplies both." So i need that SD and meter drop to be able to supply 200.

Doesn't main breakers also effectively protect the SD and meter drop?
no.... protection would need to be upstream to protect that stuff
 
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
This is not why Im here, so I should just let that be, but once breaker triggers Im no longer pulling power thru the SD. Effectively protecting it from being over drawn.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
There is no overcurrent/short circuit protection on the secondary of the PoCo transformer, so be cautious around them.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,708
Location
NW Iowa
I am at a loss as to what the question really is, but I'm going to guess that it's "What size service do I have?" Post #23 states there are two 100 amp panels with #4 service entrance to individual meters. It's a 200 amp service. You can't base it on the POCO wires, they can do whatever they want, and in free air, wires can handle a helluva lot more current than if they are in conduit or buried. The conductors in the mast look like they are at least a 2/0 and if those are copper are what a 200 amp residential service uses. It's fine.

And the POCO doesn't care about what's in the mast, those are your wires. If you really, really need to know exactly what you have, you're going to have to call an electrical contractor and pay them to come look at it.
Two 100 amp mains does not equal a 200A service. Could be anything in between 100-200A

Yes if they are copper it probably is a 200. In my earlier post I was thinking 1/0-2/0 aluminum.
 
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
Two 100 amp mains does not equal a 200A service. Could be anything in between 100-20A

Yes if they are copper it probably is a 200. In my earlier post I was thinking 1/0-2/0 aluminum.
so how do I know if they are copper?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
Two 100 amp mains does not equal a 200A service. Could be anything in between 100-200A

Yes if they are copper it probably is a 200. In my earlier post I was thinking 1/0-2/0 aluminum.
OK, you got me there. I forget that not everyone is me. If I'm putting in a service with two 100 amp mains, it's going to be a 200 amp service.
 

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
My question is why do you ask?
Is there a concern with your current capacity or are you planning on adding more Load?
You mention 2 "Main Disconnects" and 2 "Meters". What do those feed? 2 Living Quarters or a House and a Garage?
 
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
House and attached apartment. House built that way.

Yes i want to bdl ck on what was done in 2012 when the fuse boxes were upgraded to breaker boxes.

Yes im thinking of adding a 26a kiln. I might put it on the dryer 30a breaker witha switch so only one can be operated at a time, but not sure i need too.
 
To avoid these ads, REGISTER NOW!