Hi,
I have an existing main service entrance (200 amp) with a 100 amp 2 pole breaker serving sub-panel, (as well as a bunch of others for the house) and from that breaker I ran aluminum 1/0 X 3 + ground about 80 feet to sub panel attached to same structure. Currently all that first sub-panel serves is air conditioning compressor. Sub-panel 1 has no jumper between ground and neutral which from what I can tell of the pics on the 'sticky thread' is correct since this sub-panel is on main structure.
So far so good, I believe.
See pic of sub-panel 1.
I'm planning on building a new detached garage on same end of house where sub-panel 1 is. I want to run 80 amps / 240v to a new sub-panel 2. My plan is to add an 80 amp breaker in SP1, run 4/4/4/4 all CU from SP1 to SP2, about a 30 foot distance, underground in 2" electrical conduit, to SP2 on inside/outside? of new detached building.
(I know 50 amp to AC and 80 amp to shop is more than 100 amp which is breaker size on main panel, but there is no way I'll ever pull 80 amps in the garage at same time AC is running. I happen to have wire I bought 10 years ago that will handle 80 amps, so I figure I ought to use its capacity.)
So, my question(s) are related to ground to neutral bonding at SP2. Again, based on pics in the sticky thread, my understanding is the only difference between SP1 and SP2, is that SP2 must have a grounding rod 6 ft into earth, or be tied into rebar in new foundation (UFER).
Am I missing anything?
My area (Pima county AZ) requires adherence to 2017 NEC.
Thanks so much for your feedback.
Steve
I have an existing main service entrance (200 amp) with a 100 amp 2 pole breaker serving sub-panel, (as well as a bunch of others for the house) and from that breaker I ran aluminum 1/0 X 3 + ground about 80 feet to sub panel attached to same structure. Currently all that first sub-panel serves is air conditioning compressor. Sub-panel 1 has no jumper between ground and neutral which from what I can tell of the pics on the 'sticky thread' is correct since this sub-panel is on main structure.
So far so good, I believe.
See pic of sub-panel 1.
I'm planning on building a new detached garage on same end of house where sub-panel 1 is. I want to run 80 amps / 240v to a new sub-panel 2. My plan is to add an 80 amp breaker in SP1, run 4/4/4/4 all CU from SP1 to SP2, about a 30 foot distance, underground in 2" electrical conduit, to SP2 on inside/outside? of new detached building.
(I know 50 amp to AC and 80 amp to shop is more than 100 amp which is breaker size on main panel, but there is no way I'll ever pull 80 amps in the garage at same time AC is running. I happen to have wire I bought 10 years ago that will handle 80 amps, so I figure I ought to use its capacity.)
So, my question(s) are related to ground to neutral bonding at SP2. Again, based on pics in the sticky thread, my understanding is the only difference between SP1 and SP2, is that SP2 must have a grounding rod 6 ft into earth, or be tied into rebar in new foundation (UFER).
Am I missing anything?
My area (Pima county AZ) requires adherence to 2017 NEC.
Thanks so much for your feedback.
Steve