Typical residential UG service.
My POCO connects GEC to their meter socket neutral bus.
They do not mandate I install a separate bond from meter can to main panel.
My Main service panel is 6" away, connected by a PVC ******.
Ground bonding screw is installed on my panel neutral bus.
I also installed a second rod connected to my main panel.
I understand that electrically my neutral from panel to socket would carry fault current, in parallel w small earth current.
Question - Do I leave that as described, OR, do I ADD a bond from panel to socket in parallel w neutral?
In rural area of NO inspections.
In MN, we always ran and terminated the GEC into main disc...PVC *******, did not bond it to meter can, relied on POCO neutral bonded to meter can to act as ground bond.
Now, I am in TX, where the POCO provides and installs rod and GEC, and runs it into their meter can.
I have searched for answer to this detail question w no clear answer.
Marc
My POCO connects GEC to their meter socket neutral bus.
They do not mandate I install a separate bond from meter can to main panel.
My Main service panel is 6" away, connected by a PVC ******.
Ground bonding screw is installed on my panel neutral bus.
I also installed a second rod connected to my main panel.
I understand that electrically my neutral from panel to socket would carry fault current, in parallel w small earth current.
Question - Do I leave that as described, OR, do I ADD a bond from panel to socket in parallel w neutral?
In rural area of NO inspections.
In MN, we always ran and terminated the GEC into main disc...PVC *******, did not bond it to meter can, relied on POCO neutral bonded to meter can to act as ground bond.
Now, I am in TX, where the POCO provides and installs rod and GEC, and runs it into their meter can.
I have searched for answer to this detail question w no clear answer.