In order to not have to derate further the conductors in a run of pvc it was suggested that to get the 5 circuits required it could have 9 conductors, with one of the commons being shared.
This is residential 120v, there are 4 new 20 a circuits and 1 new 15 a circuit.
Would the best practice be to share the common from the circuit with the least load or?
A commercial electrician told me it's done all the time, just trying to be sure.
Thank You for the help.
This is residential 120v, there are 4 new 20 a circuits and 1 new 15 a circuit.
Would the best practice be to share the common from the circuit with the least load or?
A commercial electrician told me it's done all the time, just trying to be sure.
Thank You for the help.