Shocked by Ground Wire

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
Putting Light Switches(night light when OFF type) in today use 2 circuits of Menards Low Budget LED hanging Lights. While doing some rearraigning in the 120V Feed Panel I brushed my wrist across the Lighting Circuit Ground Wire and got a tingle. :shocking: Building has a 120V Feed (Black, White, Ground) only. Do those type of switches feed across the ground for the Night Light? :headscrat:confused:
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Putting Light Switches(night light when OFF type) in today use 2 circuits of Menards Low Budget LED hanging Lights. While doing some rearraigning in the 120V Feed Panel I brushed my wrist across the Lighting Circuit Ground Wire and got a tingle. :shocking: Building has a 120V Feed (Black, White, Ground) only. Do those type of switches feed across the ground for the Night Light? :headscrat:confused:

Does the switch have a neutral connection? If not then yes it would use the ground. This is why neutrals are now required by code in light switch j boxes.
 
OP
T

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
Update!
The Garage Panel is an old 3 Wire Setup With a Ground rod which feeds to a Fused Disconnect with a Ground rod at the "Bunkhouse" through a Hodge Podge of Romex and Conduit. By the time it gets distributed in there my Sperry Outlet Tester says the Hot and the Neutral are reversed!
As both of those buildings are not heated(high of 4 degrees yesterday) I had no desire to crawl around the attics looking for the problem. The Building where the Neutral was live(flipped the Neutral and Hot for now) is an Add-On at the far end of the "Bunkhouse".
Come Spring time I will have to investigate the issue more thoroughly.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Sounds like it's time for an upgraded feeder.

Reversing neutral and ground most likely won't fix the problem because they were never really flipped in the first place. What's going on is you've lost your neutral connection somewhere and something is feeding 120 V back on the neutral.

Had a call like this last month.

Outlets showed hot and neutral reversed.

Turns out neutral in the panel was loose and the transformers for the intercom were feeding 120v back on the neutral.
 

Jazz1

Well-known member
Joined
Jan 3, 2016
Messages
4,184
Location
Thunder Bay On.
Sounds like it's time for an upgraded feeder.

Reversing neutral and ground most likely won't fix the problem because they were never really flipped in the first place. What's going on is you've lost your neutral connection somewhere and something is feeding 120 V back on the neutral.

Had a call like this last month.

Outlets showed hot and neutral reversed.

Turns out neutral in the panel was loose and the transformers for the intercom were feeding 120v back on the neutral.

Spent seven hours chasing one of those gremlins last year. Turned out to be broken neutral in back of ceiling fan:wtf:
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Spent seven hours chasing one of those gremlins last year. Turned out to be broken neutral in back of ceiling fan:wtf:

yeah took me many hours too.

Customer has one of those 200a overstuff GE panels with neutral bar buried under the wire trough.

I had to open every junction box up.
 
OP
T

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
Yeah, It bugs me from the Safety stand point but like I mentioned earlier its a Deep Freeze (negative temps) at least till this coming weekend. If it warms up enough to at least not wear a coat I will be able to go searching/hunting for the problem.
 