Shop air conditioning ????

To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
That steel building in your aviatar? You cannot get an AC large enough to cool it. (well, you could, but I doubt you would want to pay the electric bill, or buy the unit).

Ceiling fans, large floor fans, and lots of cold water and such in the fridge.

Charles
 

whatuusay1

Well-known member
Joined
Jun 15, 2009
Messages
106
Agreed - to effectively cool the space You'd have to put in insulation on all walls, doors and ceiling - probably spray in for the best seal you can get. Assuming you do that You're probably best bet is going with a traditional A frame airconditioner and blower - mount it up off the ground to keep your floor space. Put a duct along the back wall that empties into your shop. If you dont want to mess with traditional ducts etc. You could get away with a dual zone minisplit (prob 24k BTU each) - space them out on the back wall or either side of your shop. I've had great luck with a 24k unit cooling our 3 car (insulated) garage without issue (easily drops the temp by 20 degrees in 15 minutes).

Keep in mind if you are talking about that large shop in your avatar - opening the door is going to cost you at least an hour of cooling capacity.

I'd spend the cash on insulation first - and then worry about trying to cool it.
 
OP
S

skyking

Well-known member
Joined
Jun 26, 2012
Messages
1,856
Location
Dallas & Tulsa
That is my shop/hangar .I just finished it and the entire building and all doors including the 40x12 hangar door has 3" of insulation. I thought maybe there was a trailer house or commercial outside unit that could be used. Would spend 5 or 6 thousand if nescessary. I didnt even put in skylites because I didn't want the heat.
 

windy

New member
Joined
Jun 30, 2012
Messages
1
If you are only cooling a 2000 square foot room you have a lot of choices. A large window unit would be the most economical. It would be best if you had a professional do heat load calculations for you so you could purchase the correct size unit.

My first question is "What about heat? Natural gas, propane or electrical?"

It makes sense to get a unit that can heat and cool. How about fumes? Are you going to weld, paint or do other shop activities where ventilation is needed?
 

Jern

Member
Joined
Jun 26, 2008
Messages
6
A large window unit will take the edge off. There's a 25,000 btu window unit (no window, just a hole in the wall!) in my 3000sf shop. Last weekend it was 100° outside, but it was about 85° inside. It's really too small and runs all the time, but it makes the shop usable.
 
OP
S

skyking

Well-known member
Joined
Jun 26, 2012
Messages
1,856
Location
Dallas & Tulsa
After posting this thread I wonder If I need to put in a/c .My hangar has 3" of insulation on every inch. My hangar door is 40'x12' plus a 10'x10' on the other side .We have had triple digit temps for a week and with a roll around swamp cooler I have been fine. It has me wondering................
 

JimL

Well-known member
Joined
Jul 12, 2005
Messages
271
Location
Indiana
We have put ac in a 9600 sqft shop. 18' ceilings. 10 ton gas pack sitting on the ground outside. Works great. Very well insulated building though.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
You problem is volume. The building is tall, and open to the roof, and these folks recommending mini-splits and such are not taking into consideration the CUBIC FEET of volume in the building.

I have 3600 sq/ft. However the building has a 16 ft eave, and a 21 ft peak, 66,600 cu ft of volume.

Apparently you done good if the insulation is such that the swamp cooler is doing the trick. I would seriously consider adding ceiling fans to push heat in the winter back to the floor. They might help you in the summer also to stir that swamp cooler air around.

Charles
 

carap

Well-known member
Joined
Aug 17, 2010
Messages
69
Location
OKC
I have a 2000' metal building with 14' ceiling in OKC. Inside the 2,000' is a 200' office and bathroom cooled with a 12,000 btu window unit. There is also a 150' room with CNC equipment cooled with a 18,000 btu terminal package unit (like a hotel room). Shop has radiant barrier and 6" of fiberglass insulation on walls and ceiling. With outside temp. of 109 today I have to do something quickly. My short term plan is to install a 28,500 BTU window unit in one of the man doors. Long term plan is to install a 5 ton wall mount package unit. Entire unit hangs on the outside wall with only two holes cut through the side wall for supply and return ducts.
 

pseudorealityx

Well-known member
Joined
Nov 10, 2009
Messages
999
Location
USA
I have a 2000' metal building with 14' ceiling in OKC. Inside the 2,000' is a 200' office and bathroom cooled with a 12,000 btu window unit. There is also a 150' room with CNC equipment cooled with a 18,000 btu terminal package unit (like a hotel room). Shop has radiant barrier and 6" of fiberglass insulation on walls and ceiling. With outside temp. of 109 today I have to do something quickly. My short term plan is to install a 28,500 BTU window unit in one of the man doors. Long term plan is to install a 5 ton wall mount package unit. Entire unit hangs on the outside wall with only two holes cut through the side wall for supply and return ducts.

The window A/C is mounted into the EXTERIOR wall of the office space, and not back into the rest of the shop space, right?
 

carap

Well-known member
Joined
Aug 17, 2010
Messages
69
Location
OKC
Yes, it vents through the exterior wall. That is the reason I used a 12K btu unit. The wall is 9" thick and that is the smallest unit I could find that had the side intake vents at that depth. I have had to replace the office unit once because some a-hole stole the condenser coil. Ruined a $400 unit to get $10 worth of scrap copper.
 
OP
S

skyking

Well-known member
Joined
Jun 26, 2012
Messages
1,856
Location
Dallas & Tulsa
I am looking at package units . I have also considered a take out home a/c unit(central air and heat) It was 111 today.
 

carap

Well-known member
Joined
Aug 17, 2010
Messages
69
Location
OKC
Skyking,
I was originally looking to put a package unit on the roof but the curb between the unit and the roof concerned me. I found the wall mount and like that option better. The wall unit is more expensive but you don't need the curb and I can do all the work myself. Check out acunitsdirect.com. I am looking at the W60A1-A unit.
 

EOC_Jason

Well-known member
Joined
Jun 25, 2012
Messages
11,388
Location
Bentonville, AR
What is the eve height of the building? If it was 16' you could *probably* squeak by with a 5-ton unit, which would keep the temp comfortable and humidity low. On really hot days (i.e. 110+) you would have to realize it would probably still be in the 80's in your shop (depending on what kind of heat you are generating inside with machinery or whatever), but still feel a heck of a lot better than outside! Also the unit would be running constantly all day long trying to keep up.

If it's a higher ceiling then you would seriously need a second 5-ton to keep things nice and cool... Or you would have to go to commercial sized units...
 

carap

Well-known member
Joined
Aug 17, 2010
Messages
69
Location
OKC
Not sure on Skykings eve height but mine is 12'. I have also already taken 350 sq' out of the equation with other cooling. If I could get the shop down to 80 and low humidity when the outside temp is 111 I would be very happy.
 
To avoid these ads, REGISTER NOW!
OP
S

skyking

Well-known member
Joined
Jun 26, 2012
Messages
1,856
Location
Dallas & Tulsa
Skyking,
I was originally looking to put a package unit on the roof but the curb between the unit and the roof concerned me. I found the wall mount and like that option better. The wall unit is more expensive but you don't need the curb and I can do all the work myself. Check out acunitsdirect.com. I am looking at the W60A1-A unit.

Nice link.First time I have seen a wall unit. A little pricey as you said.I will search through that link to educate myself. Thank you !
 

pseudorealityx

Well-known member
Joined
Nov 10, 2009
Messages
999
Location
USA
Many packaged units have sidewall discharge options, so they can be mounted on the ground next to the shop and ducted into the building. They you don't need to be as concerned about the penetration into the building vs. going through the roof.

Not a bad option if you've got room outside.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,410
Location
N CA
You need to get a "real" heat loss/gain on this building. Not doing so is hoping you can hit the hole on the rolling donut. Once you know what the load is, you can better select your options. I remain a fan of the mini-split heat pumps as they are all inverter controlled, meaning variable speed with attendant efficiency increases. Standard sizing for commercial buildings use the old rule of thumb of 400 sq ft/ton (12kbtu) of cooling. Does your foam increase or decrease that? Only the heat/loss gain program knows for sure.:thumbup:
 

BadgerBoilerMN

Well-known member
Joined
Aug 4, 2011
Messages
837
Location
Minneapolis
A proper heat load takes into account the volume, exterior surface area, windows doors, insulation and infiltration. Not to mention, orientation, inside and outside design temperatures. Oh yes, the latent, as well as sensible heat are considered. A swamp cooler may work for dry climates.

A mini-split heat pump is nearly always the most economical to operate (window shakers representing the very low end) and how "big" the space is represents just one component of heat load analysis. A properly sized AC unit will be more efficient at removing the latent heat than one that it over-sized.

5 tons, really? Why guess?
 

Attachments

  • Steel Building Cool Guy sample.pdf
    36.2 KB · Views: 65
Last edited:
OP
S

skyking

Well-known member
Joined
Jun 26, 2012
Messages
1,856
Location
Dallas & Tulsa
A proper heat load takes into account the volume, exterior surface area, windows doors, insulation and infiltration. Not to mention, orientation, inside and outside design temperatures. Oh yes, the latent, as well as sensible heat are considered. A swamp cooler may work for dry climates.

A mini-split heat pump is nearly always the most economical to operate (window shakers representing the very low end) and how "big" the space is represents just one component of heat load analysis. A properly sized AC unit will be more efficient at removing the latent heat than one that it over-sized.

5 tons, really? Why guess?

Thanks ,but that is a little over my head. I just want it cold enough to get my wifes ******* hard !
 

ksj9393

Well-known member
Joined
Jul 5, 2011
Messages
162
Location
Minnesota
As mentioned by BadgerBoilerMN earlier in this thread, there are a great many factors beyond mere room volume that go into A/C sizing. If you want a veracious answer, would need to know design delta T, wall/ceiling R values, infiltration, solar hear gain, etc.

If you want an off the cuff answer, I would say no... 18500 BTU is not likely to be too large. It may even be too small.
 

Big_Jim

Well-known member
Joined
Feb 9, 2012
Messages
191
Location
nw ct
As mentioned by BadgerBoilerMN earlier in this thread, there are a great many factors beyond mere room volume that go into A/C sizing. If you want a veracious answer, would need to know design delta T, wall/ceiling R values, infiltration, solar hear gain, etc.

If you want an off the cuff answer, I would say no... 18500 BTU is not likely to be too large. It may even be too small.

Design delta T? (Excuse my ignorance) But I have no clue what that is. I'm in the process of building the garage we are going with R38 in the ceiling & R19 in the walls with a complete vapor barrier and sound deadening on the ceiling as my Mom will be living above me and I don't want to disturb her with noise or fumes. Infiltration? Again (clueless)! As for Solar heat gain; I think you mean light from windows & radiant heat from garage doors & things? There will be no windows as I'm mostly below grade (on 3 sides). There will be one door leading to outside & one door to the inside both sealed fire doors (Code). The garage doors will be the best insulated ones I can get. I hope all this gives you a better idea of what I'm doing or at least trying to do and better help answer my question.
Thanks
Jim
 

Big_Jim

Well-known member
Joined
Feb 9, 2012
Messages
191
Location
nw ct
Oh and the wife wants me to put 2 ceiling fans in as well. Don't know if that makes a difference.
 

pseudorealityx

Well-known member
Joined
Nov 10, 2009
Messages
999
Location
USA
Delta T is the difference between 2 temperatures. For instance, some people want a garage that's just 'better than nothing', and low 80's is fine, since it's 100+ outside. Others want to be able to keep it cool like a house, mid to low 70's. Obviously you need a larger unit to push the temps down more.

100 - 80 = 20 degree delta T
100 - 75 = 25 degree delta T


Infiltration is how leaky the space is. You want to minimize the drafts, so good weatherproofing around the doors, any windows, etc.
 

Big_Jim

Well-known member
Joined
Feb 9, 2012
Messages
191
Location
nw ct
It will have radiant heat in the floor & insulated so good I'm hoping to be able to heat it with a match.:D Looking to keep it like I keep my house a cool dry 72-74 deg. year round. No excuse not to work on my hot rods then.;)
 