Shop disconnect question

Dtim

Member
Joined
Apr 16, 2020
Messages
10
Location
Virginia
After reading many threads here, I am planning on running 6/3 UF-B wire to my shop (170' run) off a 50 amp breaker in the main.

Can I use the an AC disconnect (at the link below) for a disconnect in the shop before running the wires into the 125 amp sub-panel ?

Thanks in advance.
DTim

lowes.com/pd/Eaton-60-Amp-2-Pole-Non-Fusible-Enclosed-Molded-Case-Switch-Disconnect/1114583
 
Last edited:
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,095
Location
Modesto, CA
What do you plan on running on this feeder?

170’ may be a little long.

Also, UF-b is very expensive.

3 #6 and 1 #10 in confuit would be far cheaper

You can use the disconnect linked to but why add more complexity and splices?

Why not get a subpanel with a main disconnect?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
A/C disconnects are 240V discos they have no provisions to land the neutral, I would use a panel with the provision a 2 pole breaker, they are available in indoor surface, or flush, or 3R outdoor, and a even better choice use a main breaker loadcenter.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,095
Location
Modesto, CA
A/C disconnects are 240V discos they have no provisions to land the neutral, I would use a panel with the provision a 2 pole breaker, they are available in indoor surface, or flush, or 3R outdoor, and a even better choice use a main breaker loadcenter.

Yeah i forgot to mention that.

Would need to some how splice a neutral and insulate it.

Just more unnecessary work.
 
OP
D

Dtim

Member
Joined
Apr 16, 2020
Messages
10
Location
Virginia
It's a 40 x 40 metal building general purpose personal workshop.
Typical air compressor, table saw, bandsaw, 110 welder, maybe a car lift at some point,etc and some lights.
The 125 amp main lug 8 space Murray main lug panel I already have (not hooked up) doesn't have a main breaker, my electrician buddy said I can use two of the slots and hook the input power up "backwards" through the breaker to feed the other circuits.
I'd rather not do that, so either an external disconnect switch or buy a new box.
Any suggestions on a new panel?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,788
Location
NW Iowa
It's a 40 x 40 metal building general purpose personal workshop.
Typical air compressor, table saw, bandsaw, 110 welder, maybe a car lift at some point,etc and some lights.
The 125 amp main lug 8 space Murray main lug panel I already have (not hooked up) doesn't have a main breaker, my electrician buddy said I can use two of the slots and hook the input power up "backwards" through the breaker to feed the other circuits.
I'd rather not do that, so either an external disconnect switch or buy a new box.
Any suggestions on a new panel?

Return panel and buy a common 20 space 100A panel. Generally I won't install a panel with less than 12 spaces for a building like this.
 
To avoid these ads, REGISTER NOW!
OP
D

Dtim

Member
Joined
Apr 16, 2020
Messages
10
Location
Virginia
Okay, thanks for the inputs !

change to:
100 amp main breaker sub panel
3 #6 and 1 #10 in conduit
Fed from existing 50 amp breaker

What size conduit is recommended ?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,788
Location
NW Iowa
At that distance I would use aluminum wire. Could get 100A for the same price as 50 with copper.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,300
Location
Illinois near St. Louis, Missouri
Definitely consider aluminum wire. Much cheaper even with needin a larger size. XHHW is a popular choice. wireandcableyourway.com is a place many of have used for source of wire. I would do at least 60A service maybe more. You may want to add more equipment later. 1.5" conduit can can easily handle AL wire for 100A service so even if you don't go with wire for that now you could pull it in later.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,095
Location
Modesto, CA

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,300
Location
Illinois near St. Louis, Missouri
Yes. That's good for 90A. May want to derate for voltage drop at that distance. If you go conduit all the way you can use XHHW but have to buy the individual conductors. They can put each on a separate reel. No twists so it pulls a little easier. A bit more cost. You can get smaller sizes if you don't need that much amperage.
 