I am hoping to build a small shop this year in my backyard and want to plan the electrical.

Distance is ~150ft. 60A service would be plenty, but I'll run 2-2-2-4 MHF to keep it easy and cheap.

I want to keep my portable generator (30A) in the shop and not have to move it to feed the house, so I'll need to run a separate line back for it.

I'd like to set it up to be able to support a 50A generator, which puts me at #4 aluminum. Is it worth just running another length of 2-2-2-4 MHF or is there a cheaper alternative? Could I use 2-2-4-6 for this run?

Any reason that they can't be in the same conduit? I looked at a fill calculator and it is telling me that 2.5" is adequate, but how hard would the pull be?

Thanks!
 
To avoid these ads, REGISTER NOW!
OP
M

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,408
Location
Richmond, VA
I would run separate conduits.

And are u gonna be using an interlock or transfer switch?

2" conduit the way to go, or bigger? Does that leave any room for additional wires? I'd like to have some exterior lights that can be switched from the house, so I was thinking a 15A circuit would be nice to add to one of the runs.

My main panel has an integrated 3-pole transfer switch (http://www.reliancecontrols.com/ProductDetail.aspx?XRR1003C) which is currently fed by a 30A Reliance power inlet box in the attached garage. This would get relocated to the workshop.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I'd like to have some exterior lights that can be switched from the house, so I was thinking a 15A circuit would be nice to add to one of the runs.

You are not to run multiple source power circuits to a detached structure. If the exterior lights are on the shop they will need to be powered from the subpanel in the shop and use a switch loop to the house for control. With all the fancy technology today those outside lights can be controlled from the house without running additional wiring.
 
To avoid these ads, REGISTER NOW!

checkthisout

Well-known member
Joined
Sep 5, 2008
Messages
5,232
You are not to run multiple source power circuits to a detached structure. If the exterior lights are on the shop they will need to be powered from the subpanel in the shop and use a switch loop to the house for control. With all the fancy technology today those outside lights can be controlled from the house without running additional wiring.

Yup. Zwave Plus will shoot a signal 150'
 
OP
M

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,408
Location
Richmond, VA
You are not to run multiple source power circuits to a detached structure. If the exterior lights are on the shop they will need to be powered from the subpanel in the shop and use a switch loop to the house for control. With all the fancy technology today those outside lights can be controlled from the house without running additional wiring.

Well that settles that. Thanks!
 