I'm adding a 240v 30a outlet and multiple 120v 20a outlets in the garage. I'm going to surface mount EMT. What is the minimum number of wires I need and do I need to pull a separate bare ground wire or can I use the conduit as ground? If yes on the ground wire, can everything share the same ground wire and what size do I need? I'm going to use 10AWG THHN for both 120 and 240 so I don't have to buy two size wires.

Thanks,
Jim
 
To avoid these ads, REGISTER NOW!

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,725
Location
SE Michigan
My two cents. Since you have done all the hard work of building an EMT system, put in a real copper grounding conductor, bond the metal boxes and the outlets to the copper wire.

I would buy by the foot: #10 awg black, #10 awg red.

Then: a spool of #12 black, a spool of #12 white and a spool of #12 green (whatever "spool size" is appropriate for the job plus some more) If you've done your own work up to this point, I feel certain someday you will want to expand the 120vac circuitry to accommodate something new. Copper is going to go up in price, slowly, forevermore, and you just locked in the price.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I agree with Matt. Buy the 10 you need for the single circuit by the foot and as much 10 ground as you need for it and b8uy the spools in 12 for the rest of it. You will have it for additions. Buy 500ft spools. Its a bit up front as he said but most economical.
 

bigb56

Well-known member
Joined
Jan 27, 2018
Messages
169
Location
Tucson, Arizona
If you are choose to run a grounding conductor (and you should) it must be sized for the largest circuit which in your case would be #10. Just because you are not required to run a grounding conductor does not mean you can run an undersized one if you choose to run one. Once you reach the end of the 30 amp circuits you can drop it down to #12 from that point on.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
My two cents. Since you have done all the hard work of building an EMT system, put in a real copper grounding conductor, bond the metal boxes and the outlets to the copper wire.

I would buy by the foot: #10 awg black, #10 awg red

Then: a spool of #12 black, a spool of #12 white and a spool of #12 green (whatever "spool size" is appropriate for the job plus some more) If you've done your own work up to this point, I feel certain someday you will want to expand the 120vac circuitry to accommodate something new. Copper is going to go up in price, slowly, forevermore, and you just locked in the price.

OP will need green #10 for the 30a circuit.
 