PushnFords
Active member
I just got done installing a 24K Gree mini-split in my 24x24 garage. I had everything in place except the lines then scheduled a company to come hook up the lines & finish it off. They canceled on me so I finished it off. Installed the line set, pressure checked with nitrogen, vacuumed to 372 microns & held 382 after 15 minutes so opened the valves to release the refrigerant in the condensor.
The manual says the unit is factory charged for 25' with a minimum of 10'. If going past 25' it gives an oz/ft of refrigerant to add. But it doesn't say anything about removing refrigerant if shortening the lines under 25'...I cut them to approx 14'. Am I good with the install as it is or do I need to have someone come adjust the charge?
The manual says the unit is factory charged for 25' with a minimum of 10'. If going past 25' it gives an oz/ft of refrigerant to add. But it doesn't say anything about removing refrigerant if shortening the lines under 25'...I cut them to approx 14'. Am I good with the install as it is or do I need to have someone come adjust the charge?