Should I run a separate ground wire when using metal conduit/boxes?

bucktruck

Active member
Joined
Mar 29, 2016
Messages
43
Location
NorCal
Title says it all. I'm starting to do the electrical in my garage, and have decided to go with external metal boxes and conduit mounted directly to my painted OSB walls. I like the way external wiring looks, and I like that it will give me some flexibility in the future in case I need to make changes.

The plan is to have one circuit for lights, one for 110V outlets, one for heating and A/C, a 220V circuit for the milling machine/lathe (and possibly MIG,) and a 220V circuit for the air compressor.

So, separate ground wire for each, or will the metal conduit suffice? My searches have yielded mixed results.
 
Last edited:
To avoid these ads, REGISTER NOW!

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,730
Location
SE Michigan
I personally think its best practice to ground each enclosure and wiring device with actual (green jacket) wire that's eventually tied back into the grounding bar.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
It really depends, metallic conduit is a code compliant grounding conductor, and if a separate grounding conductor is run & not done correctly a bad situation is created during a fault. If a grounding conductor is run, then only one sized to the largest circuit is required. BTW since the location is listed as Norcal, no California power company offers either 110 or 220 volts as a supply voltage, 120/240, 120/208, are the only choices.
 
OP
B

bucktruck

Active member
Joined
Mar 29, 2016
Messages
43
Location
NorCal
I personally think its best practice to ground each enclosure and wiring device with actual (green jacket) wire that's eventually tied back into the grounding bar.

That's what I ended up doing for the first lighting circuit I did tonight.

It really depends, metallic conduit is a code compliant grounding conductor, and if a separate grounding conductor is run & not done correctly a bad situation is created during a fault. If a grounding conductor is run, then only one sized to the largest circuit is required. BTW since the location is listed as Norcal, no California power company offers either 110 or 220 volts as a supply voltage, 120/240, 120/208, are the only choices.

The 110/220V thing was just for descriptive purposes, but thanks for the correction. It sounds like you are an electrician, so I appreciate the feedback.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
It really depends, metallic conduit is a code compliant grounding conductor, and if a separate grounding conductor is run & not done correctly a bad situation is created during a fault. If a grounding conductor is run, then only one sized to the largest circuit is required. BTW since the location is listed as Norcal, no California power company offers either 110 or 220 volts as a supply voltage, 120/240, 120/208, are the only choices.

You forgot 480Delta and 480Y/277 :lol: :lol: :lol:
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
You forgot 480Delta and 480Y/277 :lol: :lol: :lol:
480 delta is not available to new customers in the PG&E system, and 480/277 is not a residential voltage, although have found 277 volt lighting in a residence. :headscrat I did consider making the list a bit longer when writing the original post.
 

thecj3man

Well-known member
Joined
Sep 21, 2009
Messages
190
Location
East TN
It really depends, metallic conduit is a code compliant grounding conductor, and if a separate grounding conductor is run & not done correctly a bad situation is created during a fault.

Can you explain how to do it not correctly or give an example? I am curious since my garage has EMT conduit and grounding conductors ran from the grounding bar for each circuit.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I was working on one of my own, I think it may have been my helper at the time gonna do it all alone in some scheme and found a missing nut the other day. It was on a steel purlin, it has wires pass completely thru it, the pipe didn't have offset so I added another clamp about a foot from the box.
I don't do it in most cases in my own steel building or to a section of pipe with a handi box and recept in it and got nothing against a plastic cover.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
480 delta is not available to new customers in the PG&E system, and 480/277 is not a residential voltage, although have found 277 volt lighting in a residence. :headscrat I did consider making the list a bit longer when writing the original post.

It was a joke...
 

barnjunkie

Well-known member
Joined
Feb 3, 2015
Messages
181
Location
TN
My first house was built in 1929. It had almost no grounding conductors at all with knob and tube wiring.

I never slept very well.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
Was taken as such, I put the headscratch in because of the residential 277V. :D Just not something one would expect to find the in a dwelling.

yeah i must say in all the weirdness Ive come across over the years, Ive never found 277v in a residence.

My first house was built in 1929. It had almost no grounding conductors at all with knob and tube wiring.

I never slept very well.

The absence of grounding conductors shouldnt cause alarm.

And original UNMODIFIED K+T was actually a really good wiring method. The issue with K+T was when people modified it
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
yeah i must say in all the weirdness Ive come across over the years, Ive never found 277v in a residence.



The absence of grounding conductors shouldnt cause alarm.

And original UNMODIFIED K+T was actually a really good wiring method. The issue with K+T was when people modified it

Here is a photo of the shop panel that feeds the mother in law unit attached to the shop, the 15 KVA transformer supplies all the 120/240V power & the ITE panel is a mess too.

 