Should this ground wire be hooked up?

Tfue

Well-known member
Joined
Jul 11, 2014
Messages
171
Location
Southern IL
I'm helping my father in law add some outside plugs on his house. He has 200amp overhead service. He has a meter base and a separate 200 amp disconnect on the outside of the house. When we popped the cover off the breaker box I noticed he has 4 wire cable running from the disconnect to the breaker box. The ground is just hanging loose inside the breaker box. Is this supposed to be a 3 wire run? Or with the external disconnect is this considered a sub panel now requiring 4 wire?
 

Attachments

  • image.jpg
    image.jpg
    18.7 KB · Views: 214
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
The four wire run was correct, as the outside disconnect becomes your main, and the panel inside is technically a sub panel. Someone didn't know what they were doing. All of the neutrals belong on one bar, all of the grounds on another, the two bars are most likely strapped together somewhere, probably at the bottom, and this connecting strap should be removed. The ground bar should have a green screw run thru it to the back wall of the panel or have a short ground strap from it to the back wall of the panel. The neutral needs to be electrically isolated from the metal housing of the panel.

The bar on the bottom is the ground, it has the smaller lug, where that bare ground should be connected. Separate the bars electrically and make sure the neutral is isolated and the ground is bonded to the can. Any neutrals on the ground bar need to be re-routed to the proper neutral bar (wirenut and more wire works if needed), and same for grounds on the neutral bar, extend or re-route them to the ground bar.
 
Last edited:
OP
T

Tfue

Well-known member
Joined
Jul 11, 2014
Messages
171
Location
Southern IL
That is what I suspected. Thank you for confirming that. So just for my own knowledge when is a three wire run allowed to a breaker box? Is that only allowed when there is nothing between the meter base and breaker box?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,992
Location
Modesto, CA
That is what I suspected. Thank you for confirming that. So just for my own knowledge when is a three wire run allowed to a breaker box? Is that only allowed when there is nothing between the meter base and breaker box?

Yes. If it was meter straight to the breaker panel then the breaker panel would be considered the main service panel.

3-wire feeds use to be allowed after a fisconnect use to be allowed...

When was this wiring done?
 
Last edited:

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
If that wire exists, and there is an outside disconnect, it MUST be used.
Just the fact that the wire is there negates the old "3-wire feeder" exception due to the "no other metallic paths" rule.
 

Stuff

Well-known member
Joined
Aug 31, 2013
Messages
572
Also check the outside disconnect. It may not be connected on that end either.
 
To avoid these ads, REGISTER NOW!
OP
T

Tfue

Well-known member
Joined
Jul 11, 2014
Messages
171
Location
Southern IL
It is not hooked up at the disconnect. Good idea to look for that as well. My father in law had the house wired around 5-6 years ago.
 
OP
T

Tfue

Well-known member
Joined
Jul 11, 2014
Messages
171
Location
Southern IL
Well it looks like we have more work to do. We didn't have time to crawl around the attic today. But somewhere there is a junction. There is 3 wire AL URD wire leaving the disconnect and 4 wire SER cable entering the breaker box. I'm not sure how this transition is done yet. Also there is not a single GFCI in the house. He was told the kitchen and bathroom were fed from GFCI breakers. But upon opening the panel there are none to be found.
 
Last edited:

Slowgsr

Well-known member
Joined
Nov 14, 2014
Messages
610
Location
Southern ontario
Well it looks like we have more work to do. We didn't have time to crawl around the attic today. But somewhere there is a junction. There is 3 wire AL URD wire leaving the disconnect and 4 wire SER cable entering the breaker box. I'm not sure how this transition is done yet. Also there is not a single GCFI in the house. He was told the kitchen and bathroom were fed from GCFI breakers. But upon opening the panel there are none to be found.

No GFCI - sounds like my house.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
That is what I suspected. Thank you for confirming that. So just for my own knowledge when is a three wire run allowed to a breaker box? Is that only allowed when there is nothing between the meter base and breaker box?

That is correct, even by current code.

Need to replace with one continuous wire for safety and function. URD is not allowed inside buildings, it is Underground Residential Distrubution wire, and the insulation is not flame resistant.
 
Last edited:

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Need to replace with one continuous wire for safety and function. URD is not allowed inside buildings, it is Underground Residential Distrubution wire, and the insulation is not flame resistant.
What does the bold part mean??

And the URD does not seem to enter the building, just the outside disconnect. Then SER into the panel.
 