Silly question about Romex

Sychotix57

Well-known member
Joined
Mar 21, 2015
Messages
81
Location
Rocky Mount, NC
I want to wire my sheet metal garage, I have over 200 feet of 12gauge Romex laying around and didn't know if I could just run the Romex through the open ridges between the sheet metal and metal tube studs. Don't curse me for my ignorance.

Sent from my Pixel XL using Tapatalk
 
To avoid these ads, REGISTER NOW!

perrykw

Member
Joined
Jul 4, 2017
Messages
14
Location
Louisiana
I want to wire my sheet metal garage, I have over 200 feet of 12gauge Romex laying around and didn't know if I could just run the Romex through the open ridges between the sheet metal and metal tube studs. Don't curse me for my ignorance.

Sent from my Pixel XL using Tapatalk

Depends. I will start by saying I'm NOT an electrician, so if one says something different than what I say, go with them LOL.

Now, having said that, it somewhat depends on your locality. I know for sure that Romex has to be "protected. There are also certain guidelines regarding how often it has to be stapled/fastened for strain relief. If your walls are going to remain open, I would use THHN in conduit so you know it's protected.

Maybe someone more qualified will chime in.
 
OP
S

Sychotix57

Well-known member
Joined
Mar 21, 2015
Messages
81
Location
Rocky Mount, NC
for metal studs I've seen plastic pop in inserts that you run wire through.
I'm talking about the square tubing. It's like an enclosed carport. bfb188122dec44aa475ba077be296677.jpg

Sent from my Pixel XL using Tapatalk
 

Attachments

  • bfb188122dec44aa475ba077be296677.jpg
    bfb188122dec44aa475ba077be296677.jpg
    60.3 KB · Views: 0

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
Oh...around here it has to be not exposed. Besides how would you transition to boxes? Emt would be what I would use but you can't put Romex in it


Sent from my iPhone using Tapatalk
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Oh...around here it has to be not exposed. Besides how would you transition to boxes? Emt would be what I would use but you can't put Romex in it


Sent from my iPhone using Tapatalk

I put it in EMT anyway, in places where it would be exposed to a machine that might throw something at it. I'd map the place out with 3/4 EMT and just run your wire. You'll chew up 200' pretty quick anyway.
 

dave89iroc

Well-known member
Joined
Mar 25, 2015
Messages
706
Location
outside Detroit, Michigan USA
So in a garage, you are saying that Romex cannot be used at all?

romex in ok in a garage if run through studs, as it is intended to be covered by interior sheeting, etc., but can't be surface mounted unprotected , if surface mounted, it needs to be in conduit



for the OP, I'd just run EMT once and be done with it
 

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,834
Location
NW INDIANA
I have Romex (exposed) all over my basement and Romex (exposed) all over my garage

I have seen it this way in dozens and dozens of houses
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,706
Location
NW Iowa
I have Romex (exposed) all over my basement and Romex (exposed) all over my garage

I have seen it this way in dozens and dozens of houses

This^

Romex simply can't be run where subject to damage.Whether or not something is subject to damage is completely open to interpretation.

I think most would agree exposed romex at say 4' high IS subject to damage and not allowed but at 8' it may be fine.
 

Marctrees

Well-known member
Joined
Mar 5, 2015
Messages
6,265
Location
TX/LA border - Toledo Bend
I have Romex (exposed) all over my basement and Romex (exposed) all over my garage

I have seen it this way in dozens and dozens of houses

Yup.

I do not know what current NEC says, but that's how I did it for years as a contractor in Twin Cities.

But that was 25 yrs ago.

Wylie can chime in if Code allows exposed in garage nowadays different.

There always have been mandates on stapling distance, running boards, areas exposed to damage, etc.

IMHO, ... For the OP structure, EMT (or PVC) is best way to go.

Mostly because there are no really good ways to strap the cable in that construction style.

Again, current Code I don't know, been away from it too long. Marc
 

Cmreschke

Well-known member
Joined
Feb 15, 2014
Messages
775
Location
North of Detroit
Exposed is ok normally, subject to damage is not. As stated above that's open to interpretation. If run horizontally at 4 ft I'd say probably no go more often than not. If run vertically then I'd say lower than 18 inches is probably a no go. That's just me and what I've installed in Michigan legally.

Romex IS allowed in any and all conduits when the conduits are installed where romex is allowed (not outside).

A detached garage is still considered inside. The wiring to get to the garage is not allowed to be romex, but, the wiring in the garage can be.
 

Hot Rod Grampa

Well-known member
Joined
Jul 7, 2017
Messages
812
Location
Near Cooperstown New York
Might be able to put a 2x between studs at or near the roof. 4" square j box on metal post. 1/2" conduit down to working height. Outlet/device there. 2x would protect Romex from outside protrusions and give you a way to attach the Romex. Use solid thhn or similar in conduit.
 

tjdux

Well-known member
Joined
Feb 4, 2014
Messages
801
Location
Southern Nebraska
Not a sparky but agree with the exposed romex. Family handiman even had a semi current article about exposed romex in garage. May be worth a look up OP.

I do it in both my garage and basement. It has a lot to do with if you're smart/carefull enough to not damage it.

A second point, a good sheet metal screw will go right through most conduit anyways so how much protection are we really thinking there is there? Personally i prefer my unfinished section of basement where i can just see the exposed wiring.

Sent from my SM-G900V using Tapatalk
 

Matt Matt

Well-known member
Joined
May 11, 2017
Messages
523
Location
Ontario
Romax can be somewhat exposed, but never to the Direct outdoor elements. A 1 1/4 inch screw should never be able to hit the live line from either side if completely buried to stud. If it is exposed to the elements without threat a visual plastic (pvc) conduit can be used. If it is buried less, steel conduit should be used (and in some high-voltage situations, steel conduit is required always but you won't be able to use Romax as it is usually only rated for 300 V). Some inspectors allow for steel plate guarding if buried less than the requirement. If you're doing a new wire install, you should see what your inspector is requiring in your area.

Edit; I just went back and saw your picture, you have one of two choices from you can surface mount PVC conduit or surface mount metal conduit to the inside studs, but, if you ever insulate and finish the inside the conduit, it still has to remain surface mount on top of the finished product. But your local inspector will help you further.
 
Last edited:

Matt Matt

Well-known member
Joined
May 11, 2017
Messages
523
Location
Ontario
So in a garage, you are saying that Romex cannot be used at all?
Romax can be used 100% in a garage wall so long as a three-quarter inch hole is dead centre of the 3 1/2 stud. This applies to unfinished basement as well.

A few years ago, I was the stud'er for a Wendy's restaurant in Cleveland. The owner wanted cleaning plugs in the island. All the 2 1/2 inch studs (we installed), we had to either run Metal conduit through or replace with 3 1/2 inch studs. Surface mount was not the owners option for us in the restaurant. The inspector caught us at the right time with the right question.
 
Last edited:
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
NM cable "Romex®" cannot be used where subject to physical damage, which around here is defined up to the 8' level. IMHO, there is no way to make NM cable look decent in a metal structure, it looks dorky.
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
Romax can be used 100% in a garage wall so long as a three-quarter inch hole is dead centre of the 3 1/2 stud. This applies to unfinished basement as well.

A few years ago, I was the stud'er for a Wendy's restaurant in Cleveland. The owner wanted cleaning plugs in the island. All the 2 1/2 inch studs (we installed), we had to either run Metal conduit through or replace with 3 1/2 inch studs. Surface mount was not the owners option for us in the restaurant. The inspector caught us at the right time with the right question.

You can put the hole anywhere you want....that is what nail plates are for.
 

Matt Matt

Well-known member
Joined
May 11, 2017
Messages
523
Location
Ontario
Romax can be somewhat exposed, but never to the Direct outdoor elements. A 1 1/4 inch screw should never be able to hit the live line from either side if completely buried to stud. If it is exposed to the elements without threat a visual plastic (pvc) conduit can be used. If it is buried less, steel conduit should be used (and in some high-voltage situations, steel conduit is required always but you won't be able to use Romax as it is usually only rated for 300 V). Some inspectors allow for steel plate guarding if buried less than the requirement. If you're doing a new wire install, you should see what your inspector is requiring in your area.

Edit; I just went back and saw your picture, you have one of two choices from you can surface mount PVC conduit or surface mount metal conduit to the inside studs, but, if you ever insulate and finish the inside the conduit, it still has to remain surface mount on top of the finished product. But your local inspector will help you further.

You can put the hole anywhere you want....that is what nail plates are for.
I thought I covered that in my earlier post. Please read red.
 

Matt Matt

Well-known member
Joined
May 11, 2017
Messages
523
Location
Ontario
And it can be a 1/2" hole...
Sure It can be, but how does this help the OP? It could be a 2 inch hole, but both the electrical inspector and the building might have problems with the op situation. You might agree or disagree with me here?
 
Last edited:

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
(and in some high-voltage situations, steel conduit is required always but you won't be able to use Romax as it is usually only rated for 300 V). Some inspectors allow for steel plate guarding if buried less than the requirement. If you're doing a new wire install, you should see what your inspector is requiring in your area.

NM Cable (RoMEX) is required to be made up of 600 Volt rated conductors.
http://www.southwire.com/products/CuNMB.htm

All inspectors going by the NEC must accept steel nail plates when they come across them (it's in the Code).

And PVC conduit is used extensively by the utilities for high-voltage work

:lol_hitti
 
Last edited:

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,939
Location
Central New Jersey
I want to wire my sheet metal garage, I have over 200 feet of 12gauge Romex laying around and didn't know if I could just run the Romex through the open ridges between the sheet metal and metal tube studs. Don't curse me for my ignorance.

Sent from my Pixel XL using Tapatalk

Are to talking about the small open area between the sheet metal walls and the back side of the metal studs? Or you talking about actually running the wire inside the metal studs? Aren't the open ridges between the sheet metal siding and studs filled with the screws that hold the siding to the studs from the outside of the building? I am not exactly sure what you are referring too when you say "open ridges".

Jim
 
OP
S

Sychotix57

Well-known member
Joined
Mar 21, 2015
Messages
81
Location
Rocky Mount, NC
Are to talking about the small open area between the sheet metal walls and the back side of the metal studs? Or you talking about actually running the wire inside the metal studs? Aren't the open ridges between the sheet metal siding and studs filled with the screws that hold the siding to the studs from the outside of the building? I am not exactly sure what you are referring too when you say "open ridges".

Jim
The open areas between the sheet metal and studs. There are no screws through the open area.

Sent from my Pixel XL using Tapatalk
 
OP
S

Sychotix57

Well-known member
Joined
Mar 21, 2015
Messages
81
Location
Rocky Mount, NC
Also, I plan on hanging some galvanized sheet metal on the walls. Wouldn't that mean it wouldn't be exposed then? Just trying to save some money with material I already have. Turns out I have about 300' yellow Romex and 150' of white Romex.

Sent from my Pixel XL using Tapatalk
 

CJ7VFR

Well-known member
Joined
Jan 13, 2015
Messages
2,939
Location
Central New Jersey
The open areas between the sheet metal and studs. There are no screws through the open area.

Sent from my Pixel XL using Tapatalk

You're talking about the horizontal open areas created by the shape of the sheet metal walls?

If so, how were you thinking about attaching the romex to those areas? Cables have to be supported by some mechanical means (staples, holders, inside conduit, ect...) every 4 feet I do believe when they are run in open areas. And supported 8 to 12 inches outside a box where the cables run into the box.

Jim
 
OP
S

Sychotix57

Well-known member
Joined
Mar 21, 2015
Messages
81
Location
Rocky Mount, NC
You're talking about the horizontal open areas created by the shape of the sheet metal walls?

If so, how were you thinking about attaching the romex to those areas? Cables have to be supported by some mechanical means (staples, holders, inside conduit, ect...) every 4 feet I do believe when they are run in open areas. And supported 8 to 12 inches outside a box where the cables run into the box.

Jim
Zip ties. [emoji28]

Sent from my Pixel XL using Tapatalk
 

aka Larry

Well-known member
Joined
May 2, 2012
Messages
8,026
Location
Eastern, NC
My building is constructed just like yours and the answer is EMT. The good news is EMT is cheap, and very easy to work with.
 

Rock knocker

Well-known member
Joined
Aug 14, 2014
Messages
704
Emt would be what I would use but you can't put Romex in it

Incorrect.

Why? Because it's not outside? Do interior garages count as indoors if detached?

He was commenting on your assertion that you are not allowed to run NM in conduit. There's a lot of reasons why it is difficult, it takes up too much room and is difficult to pull. But when properly sized with appropriate conduit, it is not prohibited.

It must also not be in a wet location
 
Last edited:

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
You say you're going to cover the interior walls. End of topic. Run your Romex. No screws are allowed to penetrate any raceway or conduit in such a manner that they might snag the Romex or penetrate if there is vibration.
 

Matt Matt

Well-known member
Joined
May 11, 2017
Messages
523
Location
Ontario
NM Cable (RoMEX) is required to be made up of 600 Volt rated conductors.
http://www.southwire.com/products/CuNMB.htm

All inspectors going by the NEC must accept steel nail plates when they come across them (it's in the Code).

And PVC conduit is used extensively by the utilities for high-voltage work (defined by NEC as over 1000 volts)

:lol_hitti
I didn't realize you use NM-B to wire typical residential. NMD90?
 
Last edited:

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
He was commenting on your assertion that you are not allowed to run NM in conduit. There's a lot of reasons why it is difficult, it takes up too much room and is difficult to pull. But when properly sized with appropriate conduit, it is not prohibited.

It must also not be in a wet location

thanks I knew what he was saying. this structure looks like a carport to me. So wondering where the outdoor/indoor rule comes in. As I remember if its outside like buried it can't be used. I never would try to save a buck using romex in emt. just not worth it.
 