Can i feed my lights off a 20 amp outlet using 12 gauge to the switch box, and then 14/3 to to the lights? Or do i have to change everything to the lights to 12/3? LLights are already there, but they are on a circuit all by themselves, and there is an outlet right underneath the switch box. Thanks in advance.


Chris
 
To avoid these ads, REGISTER NOW!

thewatusi

Well-known member
Joined
Dec 27, 2013
Messages
1,256
Location
Philly Burbs
If you change the breaker for the outlet circuit to 15amp then you can. Otherwise all wire connected to a 20amp breaker must be 12awg or larger.
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,875
Location
oregon
The simple way to know what to do is remember the breaker is there to protect the WIRE. So the breaker has to be sized to protect the smallest wire.

lg
no neat sig line
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
Can i feed my lights off a 20 amp outlet using 12 gauge to the switch box, and then 14/3 to to the lights? Or do i have to change everything to the lights to 12/3? LLights are already there, but they are on a circuit all by themselves, and there is an outlet right underneath the switch box. Thanks in advance.


Chris

How many switches do u have?

If only one, then why are u using 3 conductor NM-b to feed the lights?

And if the breaker feeding the 20a outlet is 20a(which it should be), then no u cant use #14 NM-b, unless u change the breaker to a 15a rated breaker...
 
OP
M

Mike Honcho

Well-known member
Joined
Mar 17, 2009
Messages
163
Location
SE Michigan
How many switches do u have?

If only one, then why are u using 3 conductor NM-b to feed the lights?

And if the breaker feeding the 20a outlet is 20a(which it should be), then no u cant use #14 NM-b, unless u change the breaker to a 15a rated breaker...

2 3 way switches. Looks like I'll rewire the lights to. Thanks fur the help guys.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
2 3 way switches. Looks like I'll rewire the lights to. Thanks fur the help guys.

Well that changes everything.

And here we thought u were using a single pole switch.

U will need 2 conductor feeding the source switch. Past that it depends on how the switches and fixtures are connected...
 