Single Phase Circuits on 3 Phase Subpanel

cmelville42

Member
Joined
Oct 1, 2017
Messages
16
Location
Santa Cruz, CA
I have a 100A subpanel in my workshop. A 40A circuit provides L1/L2 to an American Rotary ADX20 phase converter that provides Delta 3 phase to a small sub-panel. Currently there is only one 20A 3 phase load in the panel. I would like to add a single phase 240V circuit utilizing just L1/L2, 40A for a welder. My understanding is that this is generally acceptable on a 3 phase service.

Anyone here running something similar or have advice? L1 and L2 are energized whether the converter is running or not.
Is it advisable to run the converter when the single phase circuit is in use, or is that unnecessary?
Since this is a one man shop, only one load will ever be in use at a time. The phase converter vendor is unwilling to tell me anything except 'consult an electrician'.

Thanks.
 
To avoid these ads, REGISTER NOW!

Cruzan80

Well-known member
Joined
Jul 22, 2015
Messages
4,291
Location
Denver, CO
Trying to figure out exactly what is going on. Is there a 100A 1Ph panel, that has a 40A circuit feeding the RPC? And the 3PH panel downstream of the RPC has a 20A load? If so, agree with micromind to just add the 40A welding circuit to the 100A panel.

Or is the sub panel referenced the 3ph panel, and getting power from the RPC?
 
OP
C

cmelville42

Member
Joined
Oct 1, 2017
Messages
16
Location
Santa Cruz, CA
I would do as you all suggest but there are no remaining slots in the 1Ph panel. I was hoping to avoid putting in yet another 1PH subpanel, hence the desire to simply add a 1PH circuit to the 3PH panel.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
I would do as you all suggest but there are no remaining slots in the 1Ph panel. I was hoping to avoid putting in yet another 1PH subpanel, hence the desire to simply add a 1PH circuit to the 3PH panel.
I would not use a panel supplied from a RPC for anything other then 3Ø loads.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,032
Location
NJ
Take some pics of the existing panel with cover off. Include mfr label with part number.

It may be easy to switch out the panel and get what you need now and for the future.
 
OP
C

cmelville42

Member
Joined
Oct 1, 2017
Messages
16
Location
Santa Cruz, CA
Thanks for the suggestions. Here are a couple photos of the 3PH subpanel.
 

Attachments

  • IMG_9049.JPG
    IMG_9049.JPG
    611.7 KB · Views: 34
  • IMG_9051.JPG
    IMG_9051.JPG
    712.8 KB · Views: 32

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,837
On 3 phase service yes single phase circuits are used all the time but not using a converter like that. Leave it for actual 3 phase loads only. They aren't meant to feed single phase circuits.
 
To avoid these ads, REGISTER NOW!
OP
C

cmelville42

Member
Joined
Oct 1, 2017
Messages
16
Location
Santa Cruz, CA
Here is the single phase panel. I'm not keen to switch it out. However, I do have a couple 20A 220 outlet circuits and one of them is very under utilized. I have a lot of outlets but rarely run more than 2 loads at a time on them; I could splice those in the panel and run them off a single breaker. That would provide the space for the welder circuit.
 

Attachments

  • IMG_9052.JPG
    IMG_9052.JPG
    624.5 KB · Views: 34
  • IMG_9053.JPG
    IMG_9053.JPG
    516.6 KB · Views: 31

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,243
Location
SE MI
Here is the single phase panel. I'm not keen to switch it out. However, I do have a couple 20A 220 outlet circuits and one of them is very under utilized. I have a lot of outlets but rarely run more than 2 loads at a time on them; I could splice those in the panel and run them off a single breaker. That would provide the space for the welder circuit.
Swap in some tandem breakers and you will have space for another 240V circuit.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,032
Location
NJ
Here is the single phase panel. I'm not keen to switch it out. However, I do have a couple 20A 220 outlet circuits and one of them is very under utilized. I have a lot of outlets but rarely run more than 2 loads at a time on them; I could splice those in the panel and run them off a single breaker. That would provide the space for the welder circuit.
That works for now, but what about next time? Doesn't that put you right back here?

If you provide a pic with the cover off, it may be easier than you think to do.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,032
Location
NJ
What is a 20/20 panel ?
The panel label indicates 20 spaces AND the number of circuits permitted out of it = 20. So it will not take any tandems per listing. Also gfci and afci cb's aren't available in tandems.
 