Why am I having so much trouble finding a single phase starter 5 hp 24A screamer air compressor. screamer = any compressor 3400 or higher RPM.

Be nice if it had a fuse kit for pressure sw.
 
To avoid these ads, REGISTER NOW!

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,788
Location
Northern VA
I just bought a 40A single phase starter for a 7.5HP motor. They are everywhere.
Type 5HP single phase motor starter into Google and a bazillion come up.

I'm curious why it is necessary to bridge the three phase starter for a single phase motor. The mag starter is just a relay. Single phase starter is a DPST relay, a three phase starter is a 3PST relay. The overload heater should trip if any one of the phases overheats.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
What do you mean run one of the lines through again. through the third pole?

I just bought a 40A single phase starter for a 7.5HP motor. They are everywhere.
Type 5HP single phase motor starter into Google and a bazillion come up.

I'm curious why it is necessary to bridge the three phase starter for a single phase motor. The mag starter is just a relay. Single phase starter is a DPST relay, a three phase starter is a 3PST relay. The overload heater should trip if any one of the phases overheats.

Many newer overload relay blocks also have phase loss protection. SO if you dont jumper from T2 to L3, and connect motor leads at T1 and T3, so that current is sensed on all 3 motor lugs, the phase loss protection will trip right after start up.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,722
Location
SE Michigan
Here is the basic concept of using a 3 pole starter and maintaining the overload protection for a single phase motor.



There are a couple of classes of motor starter, there's the NEMA series and the IEC series. Both work quite well but the NEMA series is built for 50 years of hard work if you ask me. Very robust devices, I have bought several, already-used and they will be here after I am just a memory.

That said the IEC series will work without trouble in a residential-duty shop for a long time. You could buy those new at Automation Direct among many sources.

Important when buying any starter is specifying the coil voltage, which is equivalent to the control voltage you'll be using.
 
Last edited:
OP
D

Dagny

Well-known member
Joined
Jul 25, 2014
Messages
2,980
Location
Northern Wi.
On line was easy. I have accounts at three supply houses.All wanted to sell me 3 phase starter at 3 times the price.
 

bczygan

Well-known member
Joined
Nov 4, 2009
Messages
22,002
Location
DETROIT! Arsenal of Scrappers
8911DPSG22V09

31nWB7zBL5L.jpg


Bill
 

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,788
Location
Northern VA
Many newer overload relay blocks also have phase loss protection. SO if you dont jumper from T2 to L3, and connect motor leads at T1 and T3, so that current is sensed on all 3 motor lugs, the phase loss protection will trip right after start up.

OK, that makes sense. Thanks. I guess the older "heater" style would not have this problem, right?
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,722
Location
SE Michigan
Thanks. I guess the older "heater" style would not have this problem, right?

Negative, Ghost-Rider ;)

The whole point of having overload protection (even the classic discrete-element heater style) is so a motor that's unattended (lets say on a rooftop) that attempts to start on single phase won't fry itself and require a really difficult rigging and replacement job (bucking a 25hp motor across a roof is not fun!)

The heaters should be sized close to the motor's FLA (full load amps). This will almost always be exceeded when a 3phase motor tries to start on 1 phase, then cannot, sits there drawing mega current with a locked rotor until the motor windings short or something else burns up. But, the discrete elements get hot, like right now (!) and trip the mechanically latched contact that's tied to a bimetal strip-type-thingie. The NC contact for the overload goes open and the relay drops out, because the coil can no longer be energized. Motor saved.

Just pointing out that the single-phase issue is present on both modern styles with a little screw adjuster to set the current trip limit AND the classic discrete heater element style where you look in a catalog table and find it needs 3pc of B86 heater to work correctly.

Same issues will also be present should you get a machine which was wired for 480v 3ph and attempt to run it on 240v 3ph, even if the motor's windings have been configured correctly to run on the lower voltage. The current is more or less doubled on the halved voltage and the overload heaters don't like this. One can run for 1-2 seconds until the overload contact opens up.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Negative, Ghost-Rider ;)

The whole point of having overload protection (even the classic discrete-element heater style) is so a motor that's unattended (lets say on a rooftop) that attempts to start on single phase won't fry itself and require a really difficult rigging and replacement job (bucking a 25hp motor across a roof is not fun!)

The heaters should be sized close to the motor's FLA (full load amps). This will almost always be exceeded when a 3phase motor tries to start on 1 phase, then cannot, sits there drawing mega current with a locked rotor until the motor windings short or something else burns up. But, the discrete elements get hot, like right now (!) and trip the mechanically latched contact that's tied to a bimetal strip-type-thingie. The NC contact for the overload goes open and the relay drops out, because the coil can no longer be energized. Motor saved.

Just pointing out that the single-phase issue is present on both modern styles with a little screw adjuster to set the current trip limit AND the classic discrete heater element style where you look in a catalog table and find it needs 3pc of B86 heater to work correctly.

Same issues will also be present should you get a machine which was wired for 480v 3ph and attempt to run it on 240v 3ph, even if the motor's windings have been configured correctly to run on the lower voltage. The current is more or less doubled on the halved voltage and the overload heaters don't like this. One can run for 1-2 seconds until the overload contact opens up.

Fixed it for you :D
 