In accordance with the FMC thread.
Before you all say I should have pulled it at once I have 2 runs of pipe so I pulled one and waiting on the other.
I pulled 4 awg THHN for the two hots. I plan on pulling one more 4 for the neutral.
Total run length from panel to Gfci breaker is 71’
The spa says 6 awg min at 75 degrees. This looks like it is for the terminal block with the 2 hots and the neutral. The ground bus is separate and looks like a typical buss you would find in a panel with about 6 holes for wire.
I am out of 4 awg and need to buy new wire.
Can I pull a 8 for ground or does it need to be 6?
It is on a 50 amp breaker.
Thanks