Sizing Breakers

morpheusmac

Active member
Joined
May 18, 2014
Messages
27
Location
Seattle, WA
I have a 400amp service at my main panel in my home and I'll be running a 125amp service out to my 48' x 28' 1300 sqft shop in the next few weeks.

I am planning the shop wiring right now and I want plenty of room for improvements in the future. I've mapped out a number of 50 amp receptacles for welders, a plasma cutter, an air compressor, and several other tools that run on 240v. In all I am looking at 10 240v breakers in the panel.

I plan on upgrading most of my equipment over time as my compressor is a smaller one, my welder is relatively small and I would like to get a smaller mill and lathe at some point. As such I am planning on wiring the 50 amp receptacles with 6/2 wire.

Is it important that I size the breakers for the current equipment that I have or can I purchase several 50amp breakers in order to avoid having to pay for the larger breakers in the future?

Thanks
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Only a couple models of factory cord and plug welders require wire that large. Any that come with 50 end are allowed to run on 50 but all don't require it. There are a few larger welders that may need 6 but may require a larger breaker and need to be hardwired. The 6 wire may be fine for some larger air comps but they also require hard wire.
5 hp requires 8 cable, 7 1/2 would need 6. Something to remember is that when minimum wire size is listed its for individual wires in pipe, sometimes single circuit, if cable is used it needs to be a size larger.
 
Last edited:
OP
M

morpheusmac

Active member
Joined
May 18, 2014
Messages
27
Location
Seattle, WA
I'll be running wire under drywall currently. Should I wait and run wire in conduit for the larger equipment later and size appropriately then?
 

Slowgsr

Well-known member
Joined
Nov 14, 2014
Messages
610
Location
Southern ontario
If you got the budget, nothing wrong with running 6/3 everywhere.

Go to a 4 11/16 box with a plaster ring under your board.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Why the odd box for the diy crowd? I like a 4x4 deep, it uses common covers and has plenty of room for these devices. They need deep although saw a cheaper version of the 6/50 now but some gfci are now thicker and need the extra room.
Personally if I was buying wire here might get a modest roll or piece of 8/2 for a compressor and maybe 1 welding and a full roll of 10/2 to do other stuff. If I absolutely had to have something bigger would add it after the fact.
 
Last edited:

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,872
Location
oregon
Nothing to say that you can't pull in a wire from the breaker box to the termination box and leave both ends un-terminated. What I can't confirm is if you can put a 20 or 30a breaker on a #6 wire? Me personally I would go with surface mount conduit for any circuits not installed in the build. It's a shop, not the living room.

lg
no neat sig line
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
Nothing to say that you can't pull in a wire from the breaker box to the termination box and leave both ends un-terminated. What I can't confirm is if you can put a 20 or 30a breaker on a #6 wire? Me personally I would go with surface mount conduit for any circuits not installed in the build. It's a shop, not the living room.

lg
no neat sig line

When you oversize the ungrounded conductors, you need to increase the size of the grounding conductor proportionally, the grounding conductor in NM cable is only 10 AWG, if you want to oversize the wiring use EMT or other approved metallic wiring method as the grounding conductor & the problem goes away.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,991
Location
Modesto, CA
I have a 400amp service at my main panel in my home and I'll be running a 125amp service out to my 48' x 28' 1300 sqft shop in the next few weeks.

I am planning the shop wiring right now and I want plenty of room for improvements in the future. I've mapped out a number of 50 amp receptacles for welders, a plasma cutter, an air compressor, and several other tools that run on 240v. In all I am looking at 10 240v breakers in the panel.

I plan on upgrading most of my equipment over time as my compressor is a smaller one, my welder is relatively small and I would like to get a smaller mill and lathe at some point. As such I am planning on wiring the 50 amp receptacles with 6/2 wire.

Is it important that I size the breakers for the current equipment that I have or can I purchase several 50amp breakers in order to avoid having to pay for the larger breakers in the future?

Thanks

whats the HP rating on the comp motor? If more than 3HP, it needs to be hardwired. a 50a nema outlet wont work.
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
This is one of those things that is raved over about the code but rarely explained as to why. I would like to hear the reasoning behind it.
But to the op, I can tell you this from experience that all the worry and fuss is highly over rated. Plans change, equipment does and I have parked a lot of money over the years in the walls based on **** I thought I would do. I piped inch where 1/2 would do in some cases, some I got right too. I mis estimated a lot of utility demand for a long time especially in regards to air and electric. Water is slightly different in my case due to distance and some irrigation and tank filling and well size but those are not so much a problem for most with limited supply.
I have 400A electric, could make it easy on 200 and would be a lot easier for backup.
 
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I really did better with my shop than I did on some other buildings with this as I didn't plan in quite so much detail and wired a lot as I went. There are still a lot of places I have 2 circuits where 1 would do. It was a lot cheaper and easier where I added as it was needed.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
With the 6/2 you will not have a neutral. That may be a problem if the tool also needs 120V. Jim

Everyone seems to suggest running a neutral to 240V equipment but if overcurrent protection is over 20A you cannot simply tap off for 120V, overcurrent protection will be required.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Not only that I cant think of a single time I ever needed it. Only things most face that has that are electric dryers and ranges, not sure about ovens for powder coat etc but I don't own any 120/240 shop stuff.
 

redidbull

Well-known member
Joined
Feb 20, 2011
Messages
322
Location
SW Connecticut
Everyone seems to suggest running a neutral to 240V equipment but if overcurrent protection is over 20A you cannot simply tap off for 120V, overcurrent protection will be required.

I was thinking more along the lines that it would maybe need it for the machine he that is being hooked up. Some dryers and stoves have the 4 pin plug bringing the neutral in. Jim
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
I was thinking more along the lines that it would maybe need it for the machine he that is being hooked up. Some dryers and stoves have the 4 pin plug bringing the neutral in. Jim

Dryers and ranges ALWAYS have a neutral. Some cooktops do not need one.
 

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
10,962
Location
Eastern North Carolina
I wired my shop into the walls except for the welder receptacles and other 240 volt circuits which were run in conduit up and through the attic and down the surface of the walls. This let me complete the shop with the 120 wiring, then I added the 240 circuits as needed, in the wire sizes needed, in the exact locations needed, as I needed them. I have 12 machines that require 240 volt.
 
Last edited:

Ohmthis

Well-known member
Joined
Jan 20, 2013
Messages
3,003
Location
Outside of Louisville KY
On the welder outlet(s), just put one outlet in, in a common area. Then make a extension cord that can get to anywhere in the shop. Most of the time your welding will not be close to your outlets. This is a much cheaper route than putting 5 outlets in to cover distance. Compressor wise, put in one circuit that will cover future expansion and pipe lines to other areas. I think the idea of changing and expanding gets blown out of proportion. If/when the time comes run some conduit and place the wiring then. You can think ahead by running some empty conduit into accessible areas (attics, outside, crawl spaces) and have an easier project when it’s required.
 