I'm picking up a radial arm saw and a cabinet saw (table saw) that are big (14") and wired for 1ph 220V. Both saws are old (1940's) and I don't know much more than that.
For the most part, I've only looked at the motor plate and where it says 115V, 17A or 230V, 8.5A, I have assumed that a 20A 240V circuit would be fine for the listed 8.5A. Seeing as these will be bigger motors, I'd like to do it properly however I'm not sure I have all of the required information to properly size a circuit. Some of these motors from the 1940's and 1950's don't have all of the info stamped on them like modern motors do.
I'm capable of looking up the tables in the nec but not having all of the info makes it a lot harder. Are there rules of thumb I can follow? What I don't want to do is put a 20A motor on a 30A circuit (or 30A on 50A, etc.).
Thanks.
For the most part, I've only looked at the motor plate and where it says 115V, 17A or 230V, 8.5A, I have assumed that a 20A 240V circuit would be fine for the listed 8.5A. Seeing as these will be bigger motors, I'd like to do it properly however I'm not sure I have all of the required information to properly size a circuit. Some of these motors from the 1940's and 1950's don't have all of the info stamped on them like modern motors do.
I'm capable of looking up the tables in the nec but not having all of the info makes it a lot harder. Are there rules of thumb I can follow? What I don't want to do is put a 20A motor on a 30A circuit (or 30A on 50A, etc.).