I'm installing a subpanel directly adjacent to the main, which will have 3 connected loads:
1. Electric Vehicle Service Equipment with a max load of 48A @ 240v. Because this is an EVSE, continuous use makes this a 60A load.
2. HVAC condenser with a nameplate MCA of 21.1A @ 240v.
3. A dedicated 15A/120v receptacle for occasional use charging the batteries in a small RV.
So, my calculated load for the subpanel is 96.1A. I plan to feed the main-lugs in the subpanel with (2) #3 THHN conductors landed to a 100A OCPD in the main panel. I would use (1) #8 THHN for the EGC.
My question is about sizing the neutral in this 240/120 split-phase system. If I understand correctly, the neutral needs only to be sized for the unbalanced load(s). The EVSE should always present a balanced load (a neutral won't even be connected to that piece of equipment). Same thing for the HVAC condenser, right? So, the only unbalanced load would be the 15A dedicated receptacle...
This would make a #14 adequate for the neutral? Is there a part of the code that further advises on or restricts this? I don't think I would put a #14 in there, regardless of what the minimum adequate size is. Probably, I would be inclined to put in at least a #8 to allow for additional unbalanced loads in a future reconfiguration of the panel.
Why not bring in a third #3, you ask? Only because this is a relatively small subpanel (GE TL412R1P) and I know from using the same model elsewhere that things get tight in there quick.
Thoughts?
1. Electric Vehicle Service Equipment with a max load of 48A @ 240v. Because this is an EVSE, continuous use makes this a 60A load.
2. HVAC condenser with a nameplate MCA of 21.1A @ 240v.
3. A dedicated 15A/120v receptacle for occasional use charging the batteries in a small RV.
So, my calculated load for the subpanel is 96.1A. I plan to feed the main-lugs in the subpanel with (2) #3 THHN conductors landed to a 100A OCPD in the main panel. I would use (1) #8 THHN for the EGC.
My question is about sizing the neutral in this 240/120 split-phase system. If I understand correctly, the neutral needs only to be sized for the unbalanced load(s). The EVSE should always present a balanced load (a neutral won't even be connected to that piece of equipment). Same thing for the HVAC condenser, right? So, the only unbalanced load would be the 15A dedicated receptacle...
This would make a #14 adequate for the neutral? Is there a part of the code that further advises on or restricts this? I don't think I would put a #14 in there, regardless of what the minimum adequate size is. Probably, I would be inclined to put in at least a #8 to allow for additional unbalanced loads in a future reconfiguration of the panel.
Why not bring in a third #3, you ask? Only because this is a relatively small subpanel (GE TL412R1P) and I know from using the same model elsewhere that things get tight in there quick.
Thoughts?