AntonLargiader
Well-known member
I'm replacing the old (long gone) underground power to an 18x18 detached garage. It's not a shop; it's just parking although I do want a 240 outlet for whatever comes up. Basically lights (maybe 200W total) and a few outlets. I occasionally use a portable air compressor out there, and the car's block heater runs in the early morning which is 1000W. We may plug in a Volt at times which can draw 12A. Worst case we see now is the Volt and the block heater running together but code might feel otherwise. Other outlet loads are pretty rare, and would be when the cars aren't plugged in. It's not a shop.
It's about 100' from the main panel in the house across the basement, down, underground and back up to the garage panel which is at this point an 8-position Eaton MLO.
The heater and the Volt look like 20A sustained. Would 10/3 UF do the trick? They are both 120V and could be on separate legs but of course that would be up to me.
Complicating this is that if we buy a Leaf in the future it could demand up to 6.6kW, requiring a 40A circuit. I don't know if it's worth doing that now.
It's about 100' from the main panel in the house across the basement, down, underground and back up to the garage panel which is at this point an 8-position Eaton MLO.
The heater and the Volt look like 20A sustained. Would 10/3 UF do the trick? They are both 120V and could be on separate legs but of course that would be up to me.
Complicating this is that if we buy a Leaf in the future it could demand up to 6.6kW, requiring a 40A circuit. I don't know if it's worth doing that now.